Oct 23, 2021
Hull, East Yorkshire
Retired Electrician
Hi just wondering if someone can help me.
I have an rcbo that keeps tripping but only when the fly earth and neutral lead on the bars it trips out.
Has this happened to anyone else.
I could just replace the rcbo as this could be faulty but don't want to do that if there could be another explanation.
Cheers in advance
Cheers in advance
Am I reading this correctly in that you've energised the circuit with neutral and earth flyleads disconnected?
As with any circuit.... you don't take the neutral out and energise the circuit.... you've then got 230v looking for a return path....
Are you connecting it to the correct neutral bar? All depends on the type of board is gone in to... is this an old split board being added to? ...
photos are good.
photos are good.
So all the power is in and when I put the fly lead earth and neutral lead in it trips
Can we see the rest of the board?
It looks to me like the board has been altered somewhat… ie so these first two slots are direct from mainswitch, the rest are through the rcd to the left….
Which means the neutral bar should be split…
Isn't that RCD to 'the left' a 2 module RCBO?
Also check the tightness of that solid neutral to the neutral bar as these are prone to working loose and burning out.
well the OP has disappeared, never mind, a shame really, it would have been nice to see this thread to the end.
Retired Electrician
Rcbo keeps tripping
Old leccy 007,
MDJ,