Just been looking at results:
Shed - how can you have a R1+R2 of that low and a Zs that high?? Hes misplaced the . I think! - He also states a 30mA RCD is installed on the shed - when clearly its not!
Hob - That must be one short run - less than a meter with 0.02ohms for R1+R2
Lights - as said above clearly C6 is longer with more points so how can it be the same value as downstairs??
Cooker - Same situation as hob - very short!
Also Zs and Ze they dont match up - considering Ze is 0.27 how can you have 2 circuits at 0.24 showing a Ze of 0.22 (though calculation) and some over circuits showing a Ze of 0.28 - I know bonding can bring it down and up but not by this amount.
I am wondering has he cooked the results??
Also all IRs - am I not right in saying that a reading of >200 Mohms is normally received from someone testing at 250v DC and not 500v DC??
There are so many mistakes.
  1. Nature of supply parameters Ze 0.27 ohms................. it's not a measurement required it is what the DNO say or the books figure for the supply type 0.35ohms
  2. Primary ocpd 130Ka for a 1361 type 2............... I thought it was 33Ka
  3. Installation at origin EEBADS.......................(I would have to ask when this cert was done) should be ADS
  4. Garage supply down as a final circuit ..............................surely a distribution circuit(unless it is only supplying one socket)
  5. Garage circuit cpc via sheath.....................should be Armour.
  6. All circuit disconnection times are wrong apart from the 2x socket circuits.
At this point I gave up.................
As for you lack of ring continuity, did you test at the point where you added your spur & did you test before adding your spur?............might have already been a spur off a spur
EEBADS as you don't know stands for Earthed Equipotential Bonding and Automatic Disconnection of Supply
I was unsure about the Ze... I thought you could use either the DNO value OR you could measure and use that. However, giving it some thought, the measured 0.27ohms actually sounds pretty high considering the DNO substation is less than 20 yards away in this case.
I tested for continuity at the board when I disconnected the ring prior to adding the new spur.
I'm pretty sure I've worked out where the break in the circuit is, I think it's due to some work my dad did years ago (moved socket in a bedroom). Just a DIY job, he's not a sparks. There's no way on earth that continuity was present when the board was installed!
The garage supply is a distribution circuit supplying a 15th edition board. I know it's a dodgy install (connection to the SWA from the house is via a taped up joint, I can only assume it was a bodge from the builders or previous owner! It's on the "to-do" list!) The fact that the guy reconnected it with a 32 ohm Zs and a taped up joint (right behind the CU) is further evidence of his incompetence...
Cheers for the explanation of EEBADS. I'm assuming it's a pre-17th edition term
Thanks spark!
I really think there needs to be a course for people doing the 17th which teaches the out-dated terms and regs!
I think you'll find there is, it's called experience lol
My route in means that my knowledge of previous editions is very limited which is why I do not yet do EICR's. Maybe when a few more additions have been and gone I will? ;)
:thumbsup
I keep the 16th ed amd1 and amd2 books, and the 16th ed OSG, as well as the 17th red book in addition to the current one to aid EICR's, I could really do with a 15th ed book too.
And a couple of the older GN's OSG's
I'd be asking firstly for details of their CPS provider to check on whether they're registered. Then I'd be asking about why they felt the need to replace a 16th CU that could quite easily (I assume) had an RCBO fitted, then the stickers, then the testing etc etc. I'd then invite them to come back and test properly and certify and if they don't it's over to Dom Littlewood with them.
well as much as i dont like this kind of goin on.....
Dominic Littlewood Trev?
last thing we need is that little goblin`s fires stoking...
If no ones hurt or dead your complaint will likely fall on deaf ears
take up your questions and concerns with the installer first and see what he has to say for himself
Sounds like just another case of an inexperienced sparky thinking hes doing the right thing with a little bit of knowledge
Probably not intentionally trying to rip you off but he's only seen a 17th edition board in the wooden bay at the college he was working in the week before he was doing your kitchen! Lol
I find that quite offensive matey. Not all of us Electrical Trainee as you like to call us (although I'm a 6 month wonder) are as thick as we are made out to be!!! At least we work to the latest regs.
(As Thom Dolby sang "At the tender age of 3 I was hooked to a machine just to keep my mouth from spouting junk.") Well, At my tender age of 4 I was soldering copper pipes together.
Very true mate.
Guess we're all going to come across stuff we've not seen before at some point, that's where this awesome forum comes in! I've probably learnt chatting on here over the past year than I would ever have learnt at college!
Elmer don't take it to heart mate, there are good and bad in all walks of life, there are good and bad 'short course trained' people, just as there are good and bad T/S people.
I may have spoke out of turn. This usually happens when I go on the Morgans spiced rum!!
Moral: Stay off the Morgans!
Thanks spark!
There is, it used to be called 2330 lvl 2&3 alongside working with experienced sparks who you can ask questions lol.
Is THAT what it says?! I couldn't read the writing at all? Excuse me for being naive, but what does it mean?!
As I understand from a quick google search, it's a pre-17th edition term. Is reference method "3" a pre-17th edition thing as well?! 5 second disconnection for 6A finals?
NO ITS NOT `PRE 17TH EDITION`..!!!
eebads still exists 411.1