Hi all, a little stuck with a couple of things.

house on a TT system with a 16mm main earth and a 100A main cut-out.
the board has a 30mA 2 pole RCD main switch and all the circuits are 60898 protected.
One of the circuits supply's the garage with a 6mm 70 degree SWA. The garage, however is large and about to be converted into living accommodation with 250mm loft insulation and cellotex on the internal walls. There is a lounge, bathroom and kitchenette. The circuits are 32A shower circuit for a max 7.36 KW shower using 10mm cable because of the insulation. A 20a radial socket circuit for the lounge sockets wired in 4mm and the same for the kitchen sockets. Lighting will be low energy and will be 6A in 1mm.
There may also be an oven fitted so the worst case will be another 32A circuit.
The Cu will be 6 usable ways and have a 30mA RCD main switch.

I intend to replace the supply cable with a 90 degree thermosetting SWA 3c 10mm, protected by a 63 A C/B
If there is a fault in the garage there will be no discrimination and the whole lot will go out and the reverse is also true
I am going to strongly recomend they change the main CU for a 17th edition type with two 61008 30mA for the house circuits and as it's a TT system a 100mA S type main switch. How should I protect the supply cable? Do I run it from a separate non RCD protected way in the CU and rely on the 100mA S type of the main switch?
 
You are correct with your theory. Personally i would as you say recommend a board change to the house to permit adequate discrimination.
Place the supply cable on a 63A MCB with 100mA S RCD. (Note you may need to up the cable to 3x16 SWA depending on the wiring method, distance and correction factors)
Terminate the garage supply into an all insulated consumer unit in the garage with 30mA RCD protection and run a separate T.T system rod. Terminate the bonding to your services if copper at your garage board.
Ensure you have no overlapping earth paths between your Rods for the house and garage.
Job is a gooden.
 
Thanks for the quick replies, the garage is detached and only three meters away the supply circuit is to be buried and will only be about 6m long. The SWA will not run through insulation save for about 60mm.
rattlehead, are you saying the 100mA S type will cover the sub main and I should use a 60898 cb in a way separate from the 30mA part of DB1?
 
One other thing, I spoke to the nic the other day and thought I should put in an extra earth rod and he said no, which when I thought about it makes sense. Are you sure it needs one as it is just another circuit. After all and the earth part of any fault current will goes back via the existing.
 
...and run a separate T.T system rod. Terminate the bonding to your services if copper at your garage board.
Ensure you have no overlapping earth paths between your Rods for the house and garage.

Why would you separate the earthing between the house and the garage? An additional rod may be a good supplement to the main rod, but why not keep all the earthing connected together?
 
One other thing, I spoke to the nic the other day and thought I should put in an extra earth rod and he said no, which when I thought about it makes sense. Are you sure it needs one as it is just another circuit. After all and the earth part of any fault current will goes back via the existing.

Yet more duff advise from the all knowing NICEIC!! The whole idea of a working TT system, is to gain the lowest stable Ra value you can!! So another Rod position which will be linked back to the existing rod position either via the sub-main earth conductor, or by a hard wire direct link between the new and existing rods will help in achieving lowering the Ra value. Now that makes far more sense doesn't it?? lol!!
 
Thanks for the quick replies, the garage is detached and only three meters away the supply circuit is to be buried and will only be about 6m long. The SWA will not run through insulation save for about 60mm.
rattlehead, are you saying the 100mA S type will cover the sub main and I should use a 60898 cb in a way separate from the 30mA part of DB1?

Yes Mate.
All this 'do you don't you add an extra rod' is splitting hairs really. Personally i would do it mainly to try and further reduce down the Zdb value in the garage. Also by adding an extra rod you are not relying on connecting the earthing conductor from the house to the shed and using that as a combined earthing and bonding conductor. Bare in mind if you use only the rod from the house supply you would need to run your bonds from the garage back to the M.E.T within the house or ensure your earthing conductor is big enough to use as a combined earthing and bonding conductor.
 
All this 'do you don't you add an extra rod' is splitting hairs really. Personally i would do it mainly to try and further reduce down the Zdb value in the garage. Also by adding an extra rod you are not relying on connecting the earthing conductor from the house to the shed and using that as a combined earthing and bonding conductor. Bare in mind if you use only the rod from the house supply you would need to run your bonds from the garage back to the M.E.T within the house or ensure your earthing conductor is big enough to use as a combined earthing and bonding conductor.

Thanks, I was feeling a bit bullied there for a moment. It is only a small part of the question, well actually it wasn't any part of the original question, I do like to make it correct though and as the existing rod hasn't got an earth pit I think I will put it in. As far as PFC not being Ra, no it's not but it is quite easy to divide by the voltage which makes the Ra 115 ohms-ie less than 200



Read more: http://www.electriciansforums.net/e...t-system-sub-main-design-2.html#ixzz2L4vUDRaZ
 
you can put in 10 rods if you want. secret is to go deep with 1 or 2, then measure Ra or Ze. additional rods may reduce the value. aim for <10 ohms. ( yes 10, not niceic 100, not IET 200, but 10 or less. )
 
All this 'do you don't you add an extra rod' is splitting hairs really. Personally i would do it mainly to try and further reduce down the Zdb value in the garage. Also by adding an extra rod you are not relying on connecting the earthing conductor from the house to the shed and using that as a combined earthing and bonding conductor. Bare in mind if you use only the rod from the house supply you would need to run your bonds from the garage back to the M.E.T within the house or ensure your earthing conductor is big enough to use as a combined earthing and bonding conductor.

Thanks, I was feeling a bit bullied there for a moment. It is only a small part of the question, well actually it wasn't any part of the original question, I do like to make it correct though and as the existing rod hasn't got an earth pit I think I will put it in. As far as PFC not being Ra, no it's not but it is quite easy to divide by the voltage which makes the Ra 115 ohms-ie less than 200

No-ones trying to bully you here!! 115 ohms is pretty much a waste of time, and if what your now planning to do includes a new additional rod, will make perfect sense too!! Use 2 X 5/8'' rods coupled together to give you 2.4m of depth to your rod position...
Now how am i to know how you tested this existing rod, and what voltage to use, the fake 230 volts or the real 240 volts?? lol!!

Have you thought about making enquires to the local DNO to find out if a PME connection is available from your service head, as has been suggested above?? Which will give you a far superior domestic earth connection than a TT system can provide...
 
Must be nice to live somewhere where you can drive a 2.4M rod in without there being a resounding clang as it hits bedrock at 500mm. Trust me to always live at the top of a hill (I have a fear of drowning).
 
Must be nice to live somewhere where you can drive a 2.4M rod in without there being a resounding clang as it hits bedrock at 500mm. Trust me to always live at the top of a hill (I have a fear of drowning).
know what you mean did however manage to drive a 2.4m rod in at a job in the middle of dartmoor the other day and got Ra of 22 ohms
 

Reply to TT system sub main design in the Talk Electrician area at ElectriciansForums.net

Similar Threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
Replies
17
Views
529
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
629
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
Yes, relatively common, especially in rural areas, once upon a time. The bare overhead lines would be hard-drawn copper and supported on porcelain...
Replies
20
Views
2K
davesparks
D
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks