All this 'do you don't you add an extra rod' is splitting hairs really. Personally i would do it mainly to try and further reduce down the Zdb value in the garage. Also by adding an extra rod you are not relying on connecting the earthing conductor from the house to the shed and using that as a combined earthing and bonding conductor. Bare in mind if you use only the rod from the house supply you would need to run your bonds from the garage back to the M.E.T within the house or ensure your earthing conductor is big enough to use as a combined earthing and bonding conductor.

Thanks, I was feeling a bit bullied there for a moment. It is only a small part of the question, well actually it wasn't any part of the original question, I do like to make it correct though and as the existing rod hasn't got an earth pit I think I will put it in. As far as PFC not being Ra, no it's not but it is quite easy to divide by the voltage which makes the Ra 115 ohms-ie less than 200

No-ones trying to bully you here!! 115 ohms is pretty much a waste of time, and if what your now planning to do includes a new additional rod, will make perfect sense too!! Use 2 X 5/8'' rods coupled together to give you 2.4m of depth to your rod position...
Now how am i to know how you tested this existing rod, and what voltage to use, the fake 230 volts or the real 240 volts?? lol!!

Have you thought about making enquires to the local DNO to find out if a PME connection is available from your service head, as has been suggested above?? Which will give you a far superior domestic earth connection than a TT system can provide...
 
Must be nice to live somewhere where you can drive a 2.4M rod in without there being a resounding clang as it hits bedrock at 500mm. Trust me to always live at the top of a hill (I have a fear of drowning).
 
Must be nice to live somewhere where you can drive a 2.4M rod in without there being a resounding clang as it hits bedrock at 500mm. Trust me to always live at the top of a hill (I have a fear of drowning).
know what you mean did however manage to drive a 2.4m rod in at a job in the middle of dartmoor the other day and got Ra of 22 ohms
 
Must be nice to live somewhere where you can drive a 2.4M rod in without there being a resounding clang as it hits bedrock at 500mm. Trust me to always live at the top of a hill (I have a fear of drowning).

Can't really say i've ever had too much of a problem, when i've driven rods in the ground myself in the UK and in Cyprus for myself and friends and some were straight 3m rods!! There's an awful lot of fractured limestone in Cyprus as well, which makes things a little more difficult at times!!
 

Reply to TT system sub main design in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Replacing DB’s with all singing all dancing RCBO’s Problem’s we have now…Existing installation consisted of DB Grd Floor.. DB 1st Floor…Grd Floor...
Replies
11
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
476
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
868

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock