Hi I have two 6mm csa cables in the loft each going back to a separate 30A mcb in the CU. One is redundant, the other goes to a broken 8.5kW shower. I want to fit a new 9.5kW shower and would like to join both 6mm cables together at a 50A dpst shower switch, then run a short length of 10mm csa cable from the switch to the shower. Can anyone see a problem with doing this. Both 6mm cables are approx same length (12m), there is a RCD in the CU.
Thanks
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Hi I have two 6mm csa cables in the loft each going back to a separate 30A mcb in the CU. One is redundant, the other goes to a broken 8.5kW shower. I want to fit a new 9.5kW shower and would like to join both 6mm cables together at a 50A dpst shower switch, then run a short length of 10mm csa cable from the switch to the shower. Can anyone see a problem with doing this. Both 6mm cables are approx same length (12m), there is a RCD in the CU.
Thanks

what do you think mikejd?

what can you see as the down sides to doing it this way....if any?
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Sounds great. You could always connect a fan to the circuit as well ; )
 
  • Like
Reactions: 4 people
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Good luck connecting 2 x 6mm cables in the isolator
 
  • Like
Reactions: 2 people
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

get a 8.5kWatt shower instead. use 1 6mm and keep insulation out of the way. sorted.
 
  • Like
Reactions: 2 people
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

The mind boggles
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

What ya gonna put on your test sheets?
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

and after further consideration, boggles again.
 
  • Like
Reactions: 2 people
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Thinking about that, could always put it down as a ring
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

2x 6mm cables wont fit into 50a switch terminals. better get a small din rail equipped enclosure and join them on a 100a isolator.
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Just a thought -

9500 / 240 = 39.6A
 
  • Like
Reactions: 1 person
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

bet a Electrical Trainee could get em in, cut some of them pesky cores out
 
  • Like
Reactions: 2 people
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

What ya gonna put on your test sheets?

This is no word of a lie .... I was once presented by a receptionist of a log-cabin park a piece of A4 lined paper that said ....

Circuits :
Sockets - Passed
Lights - Passed
Cooker - Passed

Appliances :
Fridge - Passed
TV - Passed
Kettle - Passed
Microwave - Passed
Toaster - Passed

That was when i was working for my dad before he retired, towards the end of my apprentership - The receptionist had apparantly told him if he wants to rent his log cabin out during the summer he's going to have to get an electrical test done on it - and he presented her with that lol. That's when we were called on his behalf.

Maybe the OP has something similar in mind, lol.
 
  • Like
Reactions: 1 person
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Just a thought -

9500 / 240 = 39.6A

perfectly OK till the insulation monkeys smother the cable.
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Thanks for the reply. Please help, I cant see the down side. Each of the two 6mm cables have individual 30A mcb's in the CU. The two 6mm cables fit easily into the 50A isolator switch. If somehow one cable became damaged in the future, then the current draw down the other cable would trip the other 30mcb.
What have I missed?
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

As Tele said, if it was a short run, no insulation you might get away with one cable on the limit but chuck some fluffy stuff on it and start the derating
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

:rolleyes4::rolleyes4:
Thanks for the reply. Please help, I cant see the down side. Each of the two 6mm cables have individual 30A mcb's in the CU. The two 6mm cables fit easily into the 50A isolator switch. If somehow one cable became damaged in the future, then the current draw down the other cable would trip the other 30mcb.
What have I missed?
Missed? Poor practice, non standard circuit/cable size, how to test it correctly not to mention the embarrassment of allowing any other electrical professional or inspection authority the satisfaction of outing your handy work. No argument you offer can excuse this as an electrical installation. Installation certificate would be interesting. Would you be so good as to forward us a copy?
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Thanks for the reply. Please help, I cant see the down side. Each of the two 6mm cables have individual 30A mcb's in the CU. The two 6mm cables fit easily into the 50A isolator switch. If somehow one cable became damaged in the future, then the current draw down the other cable would trip the other 30mcb.
What have I missed?

Numerous regulations which you need to comply with.
They can easily be found in the latest edition of BS7671.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW shower
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
68

Advert

Thread statistics

Created
mikejd,
Last reply from
Darkwood,
Replies
68
Views
9,639

Advert