Back to the topic in hand though, there are some codes that are subjective, but for the vast majority of them there is no argument. A compliant install is a compliant install.

Would you agree though that a compliant install can still merit recommendations for improvement? For example, a 32A type B 60898 cooker radial showing 0.25ohms Zs at the cooker connection point but a barely-passing persistent 1.1ohms at the socket outlet on the cooker isolator?
 
What's the socket being used for?
Is there any reason for it to be on a 32A RCBO other than the argument that it's not technically against the regs, or alternatively any reason why it can't be on a 20A RCBO in accordance with the OSG other than the cost of changing it?

The main question has been how you would code it for an EICR, I believe most who are installing it would protect it with 20A OCPD (diversity etc), but technically you don't have to.
 
Is there any reason for it to be on a 32A RCBO
Yes, fault protection.

other than the argument that it's not technically against the regs,
It is not 'technically' anything - it is compliant.

or alternatively any reason why it can't be on a 20A RCBO
No.

in accordance with the OSG other than the cost of changing it?
Ah. that sums it up.

The OSG is 'one size fits all' without having to think or do any sums.

The OSG is smaller than the BGB so obviously does not contain everything.
 
Yes, fault protection.


It is not 'technically' anything - it is compliant.


No.


Ah. that sums it up.

The OSG is 'one size fits all' without having to think or do any sums.

The OSG is smaller than the BGB so obviously does not contain everything.


Possibly Yes if expected load may exceed 20A

Geoffsd - daft question but - how do you individually quote sentences (as in your post)?
 
Would you agree though that a compliant install can still merit recommendations for improvement? For example, a 32A type B 60898 cooker radial showing 0.25ohms Zs at the cooker connection point but a barely-passing persistent 1.1ohms at the socket outlet on the cooker isolator?

C3 - Non-compliant with 134.1.4
 
Yes, fault protection.
I was questioning the 32A bit more than the RCBO bit - if the maximum the plugtop fuses will allow you to draw is 26A why would you 'need' a 32A OCPD, especially considering the maximum current rating of the cable is 27A?
It is not 'technically' anything - it is compliant.
This seems to be the argument - does one cable coming out of the RCBO make it a radial, or is it 'just the same as' spurring off a 32A ring final, even though it isn't the same because there isn't a ring final there?
With a 2.5mm ring you might want a 32A OCPD to avoid 'nuisance tripping' due to a larger number of sockets, but in what kind of situation would you need to be able to draw anything near 20A from one double socket? If there is a reason for needing so much current I would expect there to be a need for more sockets, which would invalidate the argument that it's 'just the same as' spurring off a 32A ring.



The OSG is 'one size fits all' without having to think or do any sums.

The OSG is smaller than the BGB so obviously does not contain everything.
This sounds like installing something not because you need it but because you've found some loophole in the regs and using it as an argument for it being 'allowed'; IMO the question should be 'why would you'?
I can't picture what it is but there might have been a good reason for doing this; on the other hand someone might have done it because as far as they knew sockets go on a 32A OCPD, in which case it should probably be changed for a 20A to avoid unnecessary confusion.
 
To throw another one in,what was the socket used for? maybe he had a welder on it if originally on a 16 or 20 amp breaker then instead of changing it for a type C he just upped the breaker to a 32A,strange but I,ve seen it done.in fact I recently had a neighbour ask if I had a 32 that he could swap as he'd used the old immersion circuit to power his welder from,every so often it would trip the breaker but not take out the 13A fuse in the plug top.I pointed out that he should leave it as a 16A but consider a type C instead of a B subject to the earth loop values of course.
 
I was questioning the 32A bit more than the RCBO bit - if the maximum the plugtop fuses will allow you to draw is 26A why would you 'need' a 32A OCPD, especially considering the maximum current rating of the cable is 27A?
I was answering that.
A 32A MCB would do the same.

This seems to be the argument - does one cable coming out of the RCBO make it a radial, or is it 'just the same as' spurring off a 32A ring final, even though it isn't the same because there isn't a ring final there?
Both. Move one of the rings to this RCBO if you would then think it acceptable and 'normal'.

With a 2.5mm ring you might want a 32A OCPD to avoid 'nuisance tripping' due to a larger number of sockets,
Ok, but on a ring your only allowed a 32A OCPD.

but in what kind of situation would you need to be able to draw anything near 20A from one double socket?
So the cable won't be overloaded, then? Q.E.D.

If there is a reason for needing so much current I would expect there to be a need for more sockets, which would invalidate the argument that it's 'just the same as' spurring off a 32A ring.
I think this is where you are confused.
Current is drawn by the load. A 32A OCPD won't allow more to 'leak' through and damage the cable.

This sounds like installing something not because you need it but because you've found some loophole in the regs and using it as an argument for it being 'allowed'; IMO the question should be 'why would you'?
I don't think anyone would design it as such form scratch but it is fully compliant with the regulations.

I can't picture what it is but there might have been a good reason for doing this; on the other hand someone might have done it because as far as they knew sockets go on a 32A OCPD, in which case it should probably be changed for a 20A to avoid unnecessary confusion.
I believe someone said 'we don't have to design for numpties'.

You could if you want.

I note (I think) no one has complained that the cable is too small.
 
coding

I wouldn't code it but would add a comment on cert to cover myself. Your only testing the system for safety as it stands at present time not what some moron might do in future, that's a slippery slope to insanity.
 
The only reason I would even consider mentioning it on the form is to prevent some misinformed electrician/whoever in the future bad mouthing me to the customer, saying that I should have picked it up as a defect.

My entry would discuss its compliance, with no recommendations.
 
Returning to an earlier poster's (somewhat overlooked?) point:-

https://www.google.co.uk/search?q=unfused+2+way+adapter&tbm=shop

Unfused 2-way adaptors readily available to buy now cheaply and which will be 'in the wild' for decades. 82 year old Mrs Scroggins buys one and plugs three 3kW heaters into her landing double socket, one for each bedroom. Potential 39A draw on a 27A cable protected by Type B 32A 60898 / 61009. Trip time at 39A is way off the curves, so in excess of 2.5 hours, if ever, during which time the cable is being exposed to about double its permitted heating power.

Yes I appreciate it's exactly the same problem if the socket is a spur off the ring.
 
Returning to an earlier poster's (somewhat overlooked?) point:-

https://www.google.co.uk/search?q=unfused+2+way+adapter&tbm=shop

Unfused 2-way adaptors readily available to buy now cheaply and which will be 'in the wild' for decades. 82 year old Mrs Scroggins buys one and plugs three 3kW heaters into her landing double socket, one for each bedroom. Potential 39A draw on a 27A cable protected by Type B 32A 60898 / 61009. Trip time at 39A is way off the curves, so in excess of 2.5 hours, if ever, during which time the cable is being exposed to about double its permitted heating power.

Mrs scrogging needs to use her noggin...... but i see what your saying !!!
 
She bought the adaptor on the high street having confirmed it was BS rated. She bought her heaters new from Argos. She has bodged nothing.
 

Reply to socket in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top