C
cmp260
my house has 100ms time delay rcd main switch. why would this have been installed in a house? is it legal?
thanks
thanks
Discuss 100ms time delay rcd on main domestic unit?g in the UK Electrical Forum area at ElectriciansForums.net
there is a 30mA Rcd half way down the bus
would this setup be acceptable for eicar or unsatisfactory?
also, there are two breakers which are lableled cooker and central heating, these are unused the wires go nowhere, , its lagacy of old house, cooker and ch are on kitchen ring now
should it fail eicar for this?
ta
Unable to locate cooker circuit but it's on an incorrectly rated MCB?high impedance on 25 on circuits 2 and 3
unable to locate cooker circuit
unable to locate water bond -no continuity to earth
100 ma TD main switch
unable to locate heating circuit
wrong size mcb on cooker circuit 40A
wrong size mcb on shower circuit with 6mm cable 50A
all these have code c2
im a bit annoyed since..
we no longer have an electric shower it runs off the combi boiler,
we have a gas hob, and the fan oven is rated low enoug for the kitchen ring,
the cooker circuit serves nothing
you say the `wires go noware`...if so...have these cables been taken out of the terminations at the board?there is a 30mA Rcd half way down the bus
ta
I'm at a loss to understand why he would code an S type RCD as a C2
What does "high impedance on 25" mean?
Aye, could be mateMaybe high impedance on ZS.
Reply to 100ms time delay rcd on main domestic unit?g in the UK Electrical Forum area at ElectriciansForums.net