25mm tails maintenance free joint

Discuss 25mm tails maintenance free joint in the Electricians' Talk area at ElectriciansForums.net

J

joehat

Do they exist, I have just inspected a job and seen 25mm tails extended under floor boards in standard Henley 25mm tails block, can you get 25mm maintenance free joints? It would this have to be made accessible eg hatch or something Ect? Which I still feel is poor as I've seen them carpeted over all the time.
 
Crimps. With supplementary insulation over it. And then inside an enclosure as there will be no mechanical protection.

New tails is really a better option.
 
Do they exist, I have just inspected a job and seen 25mm tails extended under floor boards in standard Henley 25mm tails block, can you get 25mm maintenance free joints? It would this have to be made accessible eg hatch or something Ect? Which I still feel is poor as I've seen them carpeted over all the time.

I'm not sure if you can get them or not but all maintenance free accessories should have a maintenance free logo (MF in a circle) on them.
 
Crimps. With supplementary insulation over it. And then inside an enclosure as there will be no mechanical protection.

New tails is really a better option.

I agree but after some other sparky extended them , I don't think the customer wants to pay for all the extra as its a 10ish meter run.
And probs a good half a day labor

Do wholesalers stock 25mm crimps ect
 
Last edited by a moderator:
A carpet hardly makes them inaccessible. As long as you know where the connections are. You've already found them, so note it on the report for the next guy - it could be you in 10 years time.

I've posted about this before, the plumbing regs (WRAS) don't consider things such as ceramic tiles, plasterboard, laminate flooring or basically anything you're likely to encounter in a domestic setting as a barrier to accessibility.
 
A carpet hardly makes them inaccessible. As long as you know where the connections are. You've already found them, so note it on the report for the next guy - it could be you in 10 years time.

I've posted about this before, the plumbing regs (WRAS) don't consider things such as ceramic tiles, plasterboard, laminate flooring or basically anything you're likely to encounter in a domestic setting as a barrier to accessibility.

With respect that is bxllocks.

What do plumbers know anyway??
 
A carpet hardly makes them inaccessible. As long as you know where the connections are. You've already found them, so note it on the report for the next guy - it could be you in 10 years time.

I've posted about this before, the plumbing regs (WRAS) don't consider things such as ceramic tiles, plasterboard, laminate flooring or basically anything you're likely to encounter in a domestic setting as a barrier to accessibility.

What about BS7671?
 
A carpet hardly makes them inaccessible. As long as you know where the connections are. You've already found them, so note it on the report for the next guy - it could be you in 10 years time.

Really.... so where do you draw the line?
What if there is a bed or chest of drawers on top of the carpet where the connection is? Using your logic that would be ok, just shift them.
 
A carpet hardly makes them inaccessible. As long as you know where the connections are. You've already found them, so note it on the report for the next guy - it could be you in 10 years time.

I've posted about this before, the plumbing regs (WRAS) don't consider things such as ceramic tiles, plasterboard, laminate flooring or basically anything you're likely to encounter in a domestic setting as a barrier to accessibility.

Agree with the fellers above - this is just rubbish. Daz
 
Agree with the fellers above - this is just rubbish. Daz

Actually, I have to partially agree with IzzyS. Accessibility is not defined, so there isn't really any reason to believe that it means there must be a welcome mat over the connection.
 
If there is a joint box which to access you have to move a wardrobe, lift a carpet, scrape up the underlay and then lift boards then how is that accessible? Daz
 
Just because accessible is not defined does not mean that concealing connections that are not deemed to be MF is acceptable.
I would not consider under a floor accessible in any circumstances. You have to remove part of the fabric of the building to get to it.
 
I would not consider under a floor accessible in any circumstances.

That's not really the point though. Can you state definitively that someone who believes that it is accessible (where marked up on as fitted drawings etc.) is wrong, and if so can you provide evidence based upon BS 7671 to justify this view?
 
That's not really the point though. Can you state definitively that someone who believes that it is accessible (where marked up on as fitted drawings etc.) is wrong, and if so can you provide evidence based upon BS 7671 to justify this view?

We can all manipulate the text "Every connection shall be accessible for inspection, testing and maintenance, except for the following"

Sticking it in concrete inside an armoured box that is welded shut, 200ft under the ground can still be classed as "accessible" then... It's just a matter of time and equipment.....
 
That's not really the point though. Can you state definitively that someone who believes that it is accessible (where marked up on as fitted drawings etc.) is wrong, and if so can you provide evidence based upon BS 7671 to justify this view?

Probably not.
I believe the reg should be worded "readily accessible" To avoid confusion. The IET's solution is to provide alternatives in the form of MF joints and other methods where confusion exists over an ill defined reg. Crackers !

If a joint is accessible under a floor because you can take it all up later, then by the same logic a joint under plaster is accessible because it can be dug out later, and ceilings can be taken down so that's ok too.
 
Surely its just common sense?

Without knowing the precise circumstances behind the introduction of the Regulation it would be difficult to guess precisely as to its intent.

There are commonly held views on this Regulation, but that isn't necessarily to state that it is the correct view. It will always be a matter of opinion without further clarificaftion.
 
Without knowing the precise circumstances behind the introduction of the Regulation it would be difficult to guess precisely as to its intent.

There are commonly held views on this Regulation, but that isn't necessarily to state that it is the correct view. It will always be a matter of opinion without further clarificaftion.

BS7671 seems like an endless minefield of different opinions to be honest.

IMHO if you have to cause disruption like lifting carpets and floorboards then it is not accessible. Each to their own though i suppose. :)
 
Without knowing the precise circumstances behind the introduction of the Regulation it would be difficult to guess precisely as to its intent.

There are commonly held views on this Regulation, but that isn't necessarily to state that it is the correct view. It will always be a matter of opinion without further clarificaftion.

The intent of the regulation is quite clear, that a connection that does not fall under the exceptions listed is available for future inspection, testing and maintenance so that the system may be maintained in a safe condition in line with the requirements of the EAWR.
 
The regulations are so clear that there are a proliferation of books and guidance notes with other peoples opinions that cloud the problem even more.
In the regs, one edition it's correct the next it's not. You could not make it up.
 
I would assume the term accessible within our industry would refer to the common practices done to inspect and test a property, as a whole, ripping carpets up and pulling boards up wouldn't be carried out on such an inspection so any joint that wouldn't be expected to be checked, would in my mind be classed as inaccessible, I would expect any sparky worth his salt to stick his head in the loft and check for joints etc unless its boarded out then they should be MF.

This is my opinion and based on common sense of joints that are unlikely to be checked during a routine inspection report so any chances of obvious issues that could be spotted with a visual but not picked up by testing is reduced with the use of MF joints.
 
Last edited:

Reply to 25mm tails maintenance free joint in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top