Hello all.

For years now I've used Phillips Hue smart bulbs in my 3, ceiling mounted lounge lights and have therefore never needed to switch them individually.

I've recently redecorated and moved to a light fixture that cannot take Phillips Hue smart bulbs, so I have decided to go from a 3 gang switch, to a three dimmer switch. However, when I was idly switching the light switches to see which light was which, I realised some odd behaviour, and it now throws me into doubt regarding wiring up the dimmer switches.

Lights are listed 1, 2 and 3, as per the image below named 'Lounge.jpg'. Their corresponding switches are labelled in image 'FrontOfSwitch.jpg'.

The problem is that in order to switch on lights 2, or 3, 1 must also be on. It is possible to have light 1 on, 2 off and 3 on, or light 1 on, 2 on and 3 off, but if light 1 is ever off, lights 2 and 3 will not turn on.

Is this a limitation of the wiring to the lights (i.e. they all spur off 1), or is this simply an incorrectly wired switch?

Furthermore, would it be possible to switch to a three gang dimmer switch, and be able to address each light individually?

Many thanks!
 
TL;DR
light 1 must be on, in order for lights 2 and 3 to come on, in a 3 gang switch. How do I fix this?

Attachments

  • BackofSwitch.jpg
    BackofSwitch.jpg
    151.2 KB · Views: 26
  • FrontOfSwitch.jpg
    FrontOfSwitch.jpg
    131.9 KB · Views: 26
  • Lounge.jpg
    Lounge.jpg
    134.4 KB · Views: 21
  • Wires.jpg
    Wires.jpg
    129.7 KB · Views: 26
The way you are saying it is working suggests the wires connected in L1 an L2 on switch 1 are reversed with L2 being the live and the wire to L1 is the switch wire if you isolate the lighting circuit and swap the wires round on switch 1 leaving the link wires as they are all the switches should then work independently,
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Wiltshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)
Business Name
N/A

Thread Information

Title
3 gang light switch issues, is it wired incorrectly?
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Catch_0x16,
Last reply from
Catch_0x16,
Replies
4
Views
1,112

Advert

Back
Top