Hi!

I've got a couple of 32A Wago clips. Creating a spur socket from a ring circuit with these is quite easy, but I wanted to know if it's advised from a safety standpoint?

When wiring an electrical socket, having these as opposed to having multiple cables going into the holes in the socket?

Would this also work in spurs within radial circuits?

thanks!
 
Try the mk lever action socket these have the equivalent of wago built in them
 
Try the mk lever action socket these have the equivalent of wago built in them
Right, but I already have some wago switches from a previous project that I'd like to use somewhere
 
This is exactly what wagos were designed for, so safety isn’t an issue.
 
This is exactly what wagos were designed for, so safety isn’t an issue.
My wagos say 32A on the side. Would a 32amp limit make any difference for electrical socket use?
 
their is no advantage in using them for a spur from a ring, the socket terminals are designed to take 3 x 2.5mm cables and often more than that.
adding extra joints in any electrical system is bad practice (in my opinion) when they are not required.
 
  • Like
Reactions: FatAlan and lilimop
For a ring final circuit they would only need to be rated at 20A.
 
Always use the 32A+ ones on 32A ring circuits, if there is a fault in the ring then both 'halves' of the ring are attached to a 32A supply. The little 20A max push-fit ones are great for lighting but I wouldn't use them on a ring.

Have you seen the double sockets with wago's on the back? They look awesome in the wholesalers until you see the price difference, they all have triple wago's on designed for spurring
 
apart from anything else, its the approximate rating of 2.5mm cable enclosed in conduit or a wall.
also, often the rating of a terminal on a standard socket.
 
  • Like
Reactions: nicebutdim and DPG
Not checked but conductors used for a ring final circuit should be rated no less than 20A therefore any connectors employed should be rated alike.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Ireland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
Ireland
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
32A Wago clips for an electrical socket spur?
Prefix
N/A
Forum
Electrical Tools and Products
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
lilimop,
Last reply from
westward10,
Replies
10
Views
2,009

Advert