can some of you installation guys enlighten me a little on borrowed neutrals?
i was changing a rcd socket outlet in the factory today which was spurred from a water metering control panel, switched the mcbs in the panel and the supply from dist. board, checked for dead, ok, but when the wires were diconnected from the old socket i found out the hard way, 230V appeared between neutral and earth?
could this be supplied from a lighting circuit? ideas please.:confused:
 
Sounds like he did follow safe isolation procedures, tested dead when shut down but then got a bolt from the natural to cpc/earth. That's the puzzle.
we are taught on the 2330 that safe isolation consists of testing:

between phase and neutral
between phase and earth
between neutral and earth.

(also the standard testing of the known and accurate device and using a proving unit)
 
Last edited by a moderator:
we are taught on the 2330 that safe isolation consists of testing:

between phase and neutral
between phase and earth
between neutral and earth.

(also the standard testing of the known and accurate device and using a proving unit)

as paul.m pointed out, i tested dead, which is what you describe as being taught in class, and this would still not have highlighted my painful experience. the voltage appeared after testing and only when neutral and earth where disconnected from their terminations, the very reason i'm asking for suggestions.
 
jaresquire,that is correct, i also made and installed the panel a few years ago (utilising the supply from the old panel) so i know its wired proper and there is no polarity issues as the electronics wouldn't work.
 
water damage, couldn't reset the trip coil, have troubleshooted this panel in the past with no issues, if i get the time i'll figure it out, probably wont be til next time someone gets a blast, the joys of industry, thanks for all the replies.
 
It's a long shot but is there a sneaky UPS incorrectly installed somewhere? You would usually hear a squealing noise though when the power goes off.
 

Reply to borrowed neutral?? in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock