can some of you installation guys enlighten me a little on borrowed neutrals?
i was changing a rcd socket outlet in the factory today which was spurred from a water metering control panel, switched the mcbs in the panel and the supply from dist. board, checked for dead, ok, but when the wires were diconnected from the old socket i found out the hard way, 230V appeared between neutral and earth?
could this be supplied from a lighting circuit? ideas please.:confused:
 
potentially! only way to tell is kill the lights as well, see if it disapears...! but why would you suggest lights?? with out physically looking at the set up it would be hard to tell you any more correct info!?
 
steve, as im sure you know i couldnt plunge productions lines into darkness, when i got the job done (don't ask!), this voltage disappeared, i remembered ( i think) reading on here about borrowed neutrals on lighting circuits in domestic premises meaning having to kill 2 circuits to make safe? i might have dream't that though?
 
Problem does not sound like a borrowed neutral. I will have a bit of a think about this.
 
MAYBE!! Just Maybe

you have a faulty MCB (that did not turn off) and the supply is crossed at some point!!!

just making it up as i go along now!!
 
MAYBE!! Just Maybe

you have a faulty MCB (that did not turn off) and the supply is crossed at some point!!!

just making it up as i go along now!!

funny you should say that, thats what i thougt and found 50 odd volts at the wrong side of one of the mcbs, so told myself to man up, then got the good news again!:mad:
 
No sorry, can't think of anything sensible, but something must have still been turned on.
 
Long shot in the dark but could it be that in the control panel you have got another energized circuit not being fed from that dis. board? It has to be coming from somewhere. Or does the neutral come from another dis board and polarity is crossed over? Pity its not a house, just turn the lot off, back on one at a time.
 
Sounds like you did not follow the correct procedure in the OSG for safe isolation - LOL
Only joking anyhow! we are continually being drummed in about safe isolation at college.
 
Sounds like you did not follow the correct procedure in the OSG for safe isolation - LOL
Only joking anyhow! we are continually being drummed in about safe isolation at college.

Sounds like he did follow safe isolation procedures, tested dead when shut down but then got a bolt from the natural to cpc/earth. That's the puzzle.
 
can some of you installation guys enlighten me a little on borrowed neutrals?
i was changing a rcd socket outlet in the factory today which was spurred from a water metering control panel, switched the mcbs in the panel and the supply from dist. board, checked for dead, ok, but when the wires were diconnected from the old socket i found out the hard way, 230V appeared between neutral and earth?
could this be supplied from a lighting circuit? ideas please.:confused:

A borrowed neutral does not only happen or come from lighting circuits. some one could have borrowed a neutral for another socket or anything really. When you had the panel isolated that fed this socket did you test for this voltage between neutral and earth at the panel?
 
I’m with you Paul. The most logical explanation would be a remote control or monitoring circuit which is feed from somewhere else. There would be no sense in borrowing a neutral for some lights or a socket from a water metering control panel. Well now that he’s got all our juices going, I believe he should go beyond the call of duty to track the gremlins down so we can sleep easy at night….lol :D
 
I work in a factory and have often noticed when working on lighting circuits that if you touch neutral to an earth there is a spark. [despite having the breaker out for that circuit] Never had a belt, though I am cautious not to touch the neutral ! Assumed it was either capacitance in the circuit or a circuit that was still on was using the same neutral.
 
Have noticed sparking neutrals myself. Have always assumed it to be the passage of electrons. (as opposed to charge).
 
A borrowed neutral does not only happen or come from lighting circuits. some one could have borrowed a neutral for another socket or anything really. When you had the panel isolated that fed this socket did you test for this voltage between neutral and earth at the panel?

yes of course i tested neutral/ earth, like i said, it only appeared once the wires were disconnected, and disappeared when reconnected (all still isolated i thought). i have encountered a live neutral a few times before and it is always the result of an open circuit, ie, a neutral out of its termination further along the line, i'm now wondering have i disturbed something from another circuit which shouldn't be connected to this?
as for further investigation, will do if i ever get the time!
 

Reply to borrowed neutral?? in the Australia area at ElectriciansForums.net

Similar Threads

During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
650
Hi everyone, I want to repurpose an old cable that was previously used to power a 3-phase machine. The cable is 4L1.5 micc, and I don't want to...
Replies
7
Views
1K
Just interested in peoples thinking on using the neutral through the earthing system like I came across today. I've come across many wrong...
Replies
10
Views
2K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
467

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock