Well I tried it on another circuit. One with a 13A "non-ring" socket on on a 16A MCB with an overall RCD on the consumer unit. the MCB did not trip but the 30ma RCD did. Suggests it the earth leakage causing the problem?
The whole thing - disconnected mains input to wall thermostat and connected 240v via fused 13A plug / flying lead to thermostat / heating pad. Capped of 240 leads from 6A RCBO during test.
The whole thing - disconnected mains input to wall thermostat and connected 240v via fused 13A plug / flying lead to thermostat / heating pad. Capped of 240 leads from 6A RCBO during test.