Situation DNO supply into garage outside meter box, submain into house approx 10M in concentric cable. Fused down by 80 swfcu . I dont know the size but it has 7 neutral strands and approx same cpc strands. Any thoughts on this.? Is it ok? I would have thought ok as same if not very similar to DNO use, just unsure where it relates to concentric in bs7671
 
Is it concentric or split concentric? If its concentric you have a problem as it will be CNE which is obviously a big no no.
 
I too have split concentric from meter to CU in my house. Nowt wrong with it if terminated well.
That said, I am probably going to swap it out for SWA when an opportunity arises.
 
Up to and including 16mm its 7 neutral stands, 25mm 11 neutral strands. Approx overall diameter 12.9mm for 10mm, 15.2 for 16mm. With regards to being buried in walls, floors or walls made of metal portioning should be treated the same as T&E where RCD protection is concerned. With CCC I've heard its similar to SWA but most data you find online will be for 90 degree not 70 degree. Probably best to ping an email to a few manufacturers or phone your scheme tech line and let them do the donkey work :)
 
Makes sense to treat it as t&e lee. The cable disapears down through dno box buried through garden then flies in through back of cu no gland in dno box either just floats into a sw fuse! Very poor but hesitant to make a big deal of it to this new customer as may come accross wrong! But deffo poor install
 
Yes, unfortunately the standard that applies to split concentric cable, is not one that allows it to be used to comply with 522.6.101 (I).
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

bigspark17

Arms
-
Joined
Location
wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Concentric cable used as submain?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
bigspark17,
Last reply from
Deleted member 26818,
Replies
6
Views
9,519

Advert

Back
Top