I need to run an out door supply.
However the dist board is boxed in.
There is access back entry but that doesn't help glanding a swa.
Could you gland outside to a through box them carry the same cable to the breaker?
Taking an earth leas from the conduit box also.
Depending on the fixed load a 2.5mm off a 32amp mcb is no different than spurring off the ring final directly from the Mcb at the consumer unit.
If overload protection isn't required then all the 2.5mm needs is fault protection which the mcb will give.
I personally would size the mcb so Ib<In<Iz but it wouldn't necessarily be a non compliance
It is different to a 2.5mm spur from a ring, this is a dedicated circuit to a single appliance and the spur from a ring is one point out of a number of points for general use. The ring circuit relies on loads being spread around the circuit to work correctly and it is advised that fixed loads greater than 2kW aren't fed via a ring circuit.
Yes you could prove by calculation that the mcb will provide fault protection for the cable, but this seems like an over the top and unnecessary thing to do for a domestic installation. Especially when you can guarantee that anyone who looks at this installation in the future will label you as a cowboy for having done it that way.
Far simpler to install an ocpd which is better matched to the load.
I hope you do realise that I'm not suggesting that it's spurred from the ring circuit, more suggested that if it was supplied from a 32 amp mcb on its own dedicated radial then as it's a fixed load it not necessarily no compliant as people are suggesting.
As stated I wouldn't use a 32 amp on a 2.5 , mearly suggesting it's no different being protected by a 32 amp as a spur is directly from the consumer unit when overload isn't a factor.
And yes the mcb will protect against fault protection you don't need a calculation to work that out.
Even a generic I2t let through value from a manufacturer will tell you that for a disconnection time under 0.1 of a second