Hi All
I have got to quote for a distribution circuit to a garage Cu.
My Question is if you bury the cables in the wall how can you provide the 30mA protection required for that cable and still achieve discretion because the garage board will also have a 30mA RCD.
Do you just provide the 30mA protection from the board in the house and have a main switch Cu in the garage?
Hope this makes sense i've had a long day!
Many Thanks
if you have a 30mA rcd in the house then no need to put one in the garage. if feeding the garage with swa the you can take it from a non rcd way and put a rcd at the garage end
ya -you should use swa or whatever appropriate installation method so you don't have to rcd the sub-main
that way the rcd is 'local' to the final circuits it's protecting and you don't have the walk back to house and lights+sockets tripping together etc. etc.
I would even come with the statement that they dont exist due to the fact that it is 30 ma and all 30 ma range is supposed to trip within 40 ms. Time delay is on 100 ma and up as some have mentioned.​
Also to comply with the requirements for additional protection, which is what the aim is here, a 30mA RCD must trip within 40mS @ 150mA. So no S type RCD would comply no matter what it is rated at.
They do exist but as already mentioned the installation wouldn't comply as the time delay would mean max trip times exceeded - Refer to Appendix 3 - table 3A with also reference to 415.1.1 as it seems to confuse so many so i have supplied the regulations, i had a lengthy debate on here explaining to a member why his submains didn't comply and after many lengthy posts i pointed out the regs to which all replies stopped. :) ...