daiplayer

Hi all

Having a strange problem with some testing .

Did an installation for somebody and upon testing discovered high Ze . ( 640 ohm )

Not happy with result ( after testing all other earthing conductors to infinite ohm or higher than 640, bonding no doubt), i discovered the earthing conductor was not connected to an earth rod, neither is there a rod to be found.
ok....so replace earth rod and conductor .

However im also getting some funny voltages accross the board. I did some ir testing to see why it is that somebody has discconected the earth ( possible earth fault ) , all good other than one mcb . Mcb of course was off ( as were all the other plus the main switch) however i was picking up flucuating voltages between the L ( at the top of the breaker which was off ) and earth of 105v , 50v, 96v , 12v, and kept on fluctuating .

The supply voltage seems fine L-N , 230Vac.

I cant understand why there could be voltages appearing on the earth or the live to the breaker when the dp main switch, rcd , all mcbs, were off ? any ideas ?
 
thats what im wondering , dodgy tester ? :-/ , however it only seems to do it on this one single circuit. . could dodgy batteries do that then ?
 
try using an analogue voltmeter/multimeter. and what's the Ze now you have reinstated the earthing?
 
i havent done the earth rod yet . the house is unoccupied at the moment so ive left it all off. ( was 8pm last night )
 
Yeah if there is a broken earth then your digital meter will pick voltages up like that. Think it's called capacitive coupling.
 
Yeah if there is a broken earth then your digital meter will pick voltages up like that. Think it's called capacitive coupling.

Well thats a new one on me ....:-) as they say , learn something new everyday. :-)

- - - Updated - - -

Or, put a 230V lamp in parallel with your Digital meter.

i did that yeah. i did it with the multifunction, then with my fluke voltage indicator , and it showed the same.
 
ok further note..... wandering around the board with my voltage indicator, testing everywhere for funny voltages.

Tested between the incoming N, ( top of dp switch) and the m.e.t. .......and shows continuity.....

why would this happen ???
and before people scream TNCS ! , i did a loop test L,N, and the m.e.t. to rule this out. and shows 343 ohm. im guessing two parallel bonding conductors through the pipework .
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earthing and voltage issues
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
daiplayer,
Last reply from
daiplayer,
Replies
9
Views
1,853

Advert

Back
Top