Discuss Earthing and voltage issues in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
daiplayer
Hi all
Having a strange problem with some testing .
Did an installation for somebody and upon testing discovered high Ze . ( 640 ohm )
Not happy with result ( after testing all other earthing conductors to infinite ohm or higher than 640, bonding no doubt), i discovered the earthing conductor was not connected to an earth rod, neither is there a rod to be found.
ok....so replace earth rod and conductor .
However im also getting some funny voltages accross the board. I did some ir testing to see why it is that somebody has discconected the earth ( possible earth fault ) , all good other than one mcb . Mcb of course was off ( as were all the other plus the main switch) however i was picking up flucuating voltages between the L ( at the top of the breaker which was off ) and earth of 105v , 50v, 96v , 12v, and kept on fluctuating .
The supply voltage seems fine L-N , 230Vac.
I cant understand why there could be voltages appearing on the earth or the live to the breaker when the dp main switch, rcd , all mcbs, were off ? any ideas ?
thats what im wondering , dodgy tester ? :-/ , however it only seems to do it on this one single circuit. . could dodgy batteries do that then ?
try using an analogue voltmeter/multimeter. and what's the Ze now you have reinstated the earthing?
Yeah if there is a broken earth then your digital meter will pick voltages up like that. Think it's called capacitive coupling.
Well thats a new one on me ....:) as they say , learn something new everyday. :)
- - - Updated - - -
Or, put a 230V lamp in parallel with your Digital meter.
i did that yeah. i did it with the multifunction, then with my fluke voltage indicator , and it showed the same.
ok further note..... wandering around the board with my voltage indicator, testing everywhere for funny voltages.
Tested between the incoming N, ( top of dp switch) and the m.e.t. .......and shows continuity.....
why would this happen ???
and before people scream TNCS ! , i did a loop test L,N, and the m.e.t. to rule this out. and shows 343 ohm. im guessing two parallel bonding conductors through the pipework .
Reply to Earthing and voltage issues in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
