I have a couple of questions about testing and maintenance of emergency lights.

  1. I have been told that if the LED on an emergency light does not work it must be considered “Failed” and the fitting replaced, but when reading up, I cannot find any regulations or guidance to suggest this is correct. The documentation only talks about emergency lights working once power has been cut. Can anyone help?
  2. All lights work in maintained mode. Some lights need new batteries, but there are some lights that do not come on at all when the power is cut (LED indicates battery is charging).
    Is it best to try replacement batteries in these lights?
    Or, should I replace the emergency module as well as the battery?
  3. Any advice or experience would be welcomed.
Regards
 
Not too well up on current requirements but this is what I believe to be the case:
If the charge LED does not work then there is no way to confirm the light is charging, the easiest resolution is to replace the LED, not the fitting.
However I am not sure that it is essential to have the LED but charging should be able to be confirmed so that a faulty light can be replaced.

If the indicator light shows the batteries are charging and then the fitting does not illuminate on power failure it is likely it is just the batteries (or possibly just the battery connection). This is assuming that the lights are lit when the power is on.
 
1. The led actually shows voltage is present at the charging circuit, and is no idication that the battery is charging. If there is no led lite, there is a good chance the batteries have gone, and either taken the charging fuse or charging circuit.....So answer is investigate or replace.
2. Again investigation time, these days a new fitting is more cost effective.
3. Hope the above helped
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Amersham
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Emergency Light testing and repairs
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
Davisonp,
Last reply from
tazz,
Replies
3
Views
1,333

Advert

Back
Top