N

Namaccy97

I’m replacing emergency light fittings which have three terminals L-N-E, with new fittings which have four terminals (permanent live, switch live, neutral and earth). I only have a switch live going to these lights which is from distribution board to light switch then to these lights. Will these lights need re-wiring so that there is a permanent live to the fittings. As otherwise the switch will have to stay on so the batteries get charged.
 
Surely the existing fittings can’t be emergency without a permanent feed.
[automerge]1573981706[/automerge]
You could change the switch to a key switch that will give you a permanent feed and can also be used for testing the fittings.
 
  • Agree
Reactions: telectrix
Surely the existing fittings can’t be emergency without a permanent feed.

Surprisingly they are, they were reported as failures. That’s why im replacing them. I’m assuming the batteries were only getting charged when the light switch was on which is why these lights kept failing.
[automerge]1573981871[/automerge]
Surely the existing fittings can’t be emergency without a permanent feed.
[automerge]1573981706[/automerge]
You could change the switch to a key switch that will give you a permanent feed and can also be used for testing the fittings.

there is already test key switches there, I was thinking of connector blocking the conductors in the light switch
 
This isn't uncommon for someone to incorrectly connect them so the permanent supply is isolated by the general lighting switch. Sometimes it's an easy fix depending on how they are wired sometimes an amount of rewiring is necessary with the installation of a suitable test facility. It maybe sometimes a better solution to look at the existing general lighting to see if there is a permanent live present and replace those with em fittings, a bit of investigation is required.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Emergency light wiring
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
3

Thread Tags

Advert

Thread statistics

Created
Namaccy97,
Last reply from
westward10,
Replies
3
Views
1,502

Advert