Hi guys

turned up to a residential property today to add a few double socket outlets only to find the fuse box in the area was being fed by a ring main on the main switch. Is this allowed ?
 
So there's a main CU supplying a socket ring main which in turn supplies another fuse box....is that correct? What is the fuse box supplying?
 
3 rcbos ( 16amp with 2 double sockets 1x20amp feeding 3 double sockets, 1x6amp feeding 6 6watt led spots
 
well whats the ring thats feeds it fused at? it probably doesn't break any regs, but is liable to be overloaded and trip the MCB feeding the ring and DB.
is it an actual ring main , with sockets, or is it just a sub main wired up with 2 x 2.5mm conductors?
 
This is likely to work but not to be suitable for installation. The possibilities for overloading a cable are very real. However in normal use a socket circuit does not draw much power.
A ring final can only have a spur limited to 13A or a single double socket attached to it.
Effectively this is creating a very high current draw potential at a single point, which is not the intention for a ring final.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fusebox being fed by a ring main
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
30

Advert

Thread statistics

Created
Crazyk,
Last reply from
Guest55,
Replies
30
Views
7,310

Advert

Back
Top