M
Maddermanblue
Hi,
The builders are extending the kitchen in my house at the moment which means putting in an extra 2 double sockets. I'm doing the electrics myself. I plan to to fix an unswitched 13A FCU to the spur off the ring main and put the 2 new double sockets on it.
I have been looking at the big red book; Appendix 15, the one with the ring diagram. I'm confused on the cable sizing. The diagram in the red book coming off the main ring is an FCU with a cable size of 2.5mm but coming off the FCU to a spurred socket is a 1.5mm cable, fair enough.
In another book, (Electrical Installations 2330 Level 2) it confirms the above but it says a MINIMUM size of the conductor is 1.5mm for a fused spur (I assume you can't go lower than 1.5mm but can go higher??).
Taking 'MINIMUM' into account does that mean I can use a 2.5mm cable instead of 1.5mm cable between the FCU and the new socket? Bearing in mind I need to run a washing machine and tumble drier and possibly a fridge off it...
I'm new in the world of electrics, passsed my C&G 2330 Level 2 and other bits not long ago and trying to gain experience and break into the field.
Another certified and registered sparky is going to come and inspect and sign off my work once its done - I'm just saving face asking him a question that may seem silly...
Any advice would be appreciated.
Maddermanblue
You can do it in 2.5mm always do. The trouble you may have is the load you are planing to put on it. With an fcu you are limited to 13A and a fridge. washng machine and tumble dryer are going to be more than that. Forget the fcu ad run the spur in 4mm t/e which is ok on the 32A ring mcb
The minimum for a fused spur is 1.5mm as you rightly state.....this is because 1.5mm t/e is rated higher than 13a,the rating of the fuse protecting it.However,99% of sparks would use 2.5mm.......all that load you are proposing off a 13a spur is in the region of 20-25a all running.....Have you thought this one through?
Not acceptable as a spur from a ring, as it would result in uneven loadings on the ring cables. This would not comply with the regs.
yes you can use higher the reason you can use a 1.5mm cable is the fact that its been fused down to a max of 13 amps , and yes you can go higher , the only problem i can see with what you are suggesting is the loading if you have a fridge washing machine and tumble dryer all off a fused spur there will be a good chance the FCU is over loaded what i would suggest is that you either cut into the ring to add these sockets or install a 4mm radial circuit from the CDU to the sockets and protect by a 32 amp MCB oh and dont forget this type of work is notifiable as it falls into the special locations IE the kitchen
Nick
Nick
I agree, I thought its too much a load for a 13A FCU. So cutting into the ring, making the new sockets part of the ring is ok and complies with the regs?
Origionally in the kitchen only has 2 singles and 2 doubles at the mo...
Regards
Maddermanblue
Regards
Maddermanblue
Splitting the ring and inserting your new sockets so they are now "in" the ring would be OK and a perfectly good way of getting the "load" to the new sockets.
Hi Wirepuller
Can you point to a specific reg? I don't think it's anymore onerous on the ring than the poular kitchen grid switch which may have every appliance on it all taken from one place on the ring, not arguing just discussing. :)
No argument mate!:cool:.....appendix 15 covers what can and cant be done on a ring, 1(i) requires sharing evenly the load around the ring.
Which means that all these new builds with the lovely neat grid plate are probably non-compliant. I do remember reading something ages ago about this but can't think where it was, probably Professional Electrician or some such. Interesting thought.
Hi Wirepuller
He is looking to spur 2 sockets. Which would make this a spur off a spur. Which is not allowed
Hi Wirepuller
Possibly
If it was near mid point of the ring it would be shared equally no doubt
It has been known to assess, say for a kitchen ring, where the appliances are going, so that the ring can be installed to take the position of the loads into account
I would like to mention something here chaps but as far as I am aware you sohuld not be using 1.5 T/E cable in a ring main period. When you spur off you should use 2.5 T/E cable. If you were spuring off to a lighting circuit then from the spur you would use 1.5 T/E but beofre the spur 2.5 T/E.
As already mentioned the load would be way to much under these conditions. Just look at your appliances and add up the amps needed and you will find it is way more than 13A.
Once you have spured off you can add as many sockets as you like within under the regs but again you have to work out what you are going to plug into it.
Best bet would either be to extend the ring main or run a new cable from the consumer unit.
Hope it works out
Gerry
Says who? This is the usual fall back position. Appendix 15 is guidance, not normative and Appendix 8 of the OSG gives advice on standard cct arrangements for households. It goes on to say "cct arrangements other than those detailed in this appendix are not precluded when specified by a competent person"
I am unconvinced by the "sharing the load" arguement in a domestic situation as the lengths of cable and power demand are insufficient to significantly affect current flow.
I go back to the gridswitch example, where you can connect 4,6,8 appliances to a single point in a ring, if load sharing capabilities were the big issue then I am sure these would have been banned.
Discuss.
Don't have my BRB with me but I do have my OSG and page 159 8.2.4 says in an A1 ring final circuit and an A2 radial circuit of table 8A a non-fused spur should feed only ONE single or ONE twin or multiiple socket outlet or ONE item of permanetly connected equipment. Or am I reading this wrong??
Fused spur off a ring main cable size question
Maddermanblue,
HandySparks,