Yes it is a standard cct now but by using a 4mm spur only makes it non-standard, not wrong.
I would like to mention something here chaps but as far as I am aware you sohuld not be using 1.5 T/E cable in a ring main period. When you spur off you should use 2.5 T/E cable. If you were spuring off to a lighting circuit then from the spur you would use 1.5 T/E but beofre the spur 2.5 T/E.
As already mentioned the load would be way to much under these conditions. Just look at your appliances and add up the amps needed and you will find it is way more than 13A.
Once you have spured off you can add as many sockets as you like within under the regs but again you have to work out what you are going to plug into it.
Best bet would either be to extend the ring main or run a new cable from the consumer unit.
Hope it works out
Gerry
I was refering to truckster's advice to take a 4mm non fused spur to do the 2 sockets
I definitely agree.
If you are taking a spur from a ring, you can only have one double socket at the most. But if you are coming of a FCU then it's unlimited amount bearing in mind that your limited to 13amps.
And someone mentioned about not being able to use 1.5mm? As has been said previously. You have fused the circuit down to 13a and (off the top of my head) 1.5 can take around 26a
I really dont get why you dont just extend the ring main using a 30a junction box?
Welcome to the forum johnelectrician.
I've not read the whole thread, but the OP wanted more than one socket on the spur, so it has to be fused to prevent overloading the spur. See appendix of BS7671.
By the way, the OP has probably finished the job by now, being a year on!
or he could of just extended the ring final circuit aslong as its within 100sqm, i thoought this would of been the preffered method that putting a 13a fused spur in place?