ojbor

please could anybody explain why I am getting a high insulation test live to earth on a chandelier with 7 of the above lamps in when a lamp is removed the reading improves by 2 m ohms for each one.
 
Can understand your reason for dead testing, with lamps still installed....But the answer your question, Read up on resistors in series and parallel.
 
Thanks Tazz a workmate of mine asked me this question and don't know why he was dead testing the fitting with the lamps in but he did anyway. He was happy with the readings on the circuit minus lamps about 300 meg ohms but was interested as to reasons for the readings live to earth through the lamps and I couldn't explain. Still cant but will check up on resistors in parallel
 
what was the reading L-E in megohms with all lamps in?
 
so that's well over the "pass" value of 1 MΩ. why bother further?
 
so that's well over the "pass" value of 1 MΩ. why bother further?

Because the meter don't say >299 MOhm!


Have any of these boys ever considered how much electric is dribbling away every second of the day, and out etc... from the cables?
 
don't mention dribbling. we're all getting older daily. :ack2:
 
don't mention dribbling. we're all getting older daily. :ack2:

I'm developing a re-circ drip tray to hang around my neck, like those baby ones.
Or a more advanced version where the catchment area will plug straight into the stomach.
 
Does anybody actually know the answer to my query I could understand the explanation of resistors in parallel if the reading was live to neutral but why live to earth ?
 
what type of lamps are fitted? and what base configuration?

and 7 equal resistances in parallel will give a combined resistance of 1/7 of each.
 
Html an
 
so test from the L or N terminal to the BC base on each lamp ( with the lamp out ). see if you get a reading.
 
so test from the L or N terminal to the BC base on each lamp ( with the lamp out ). see if you get a reading.

the reading is through the lamp to earth ( some people call lamps bulbs ) ie with all the lamps in and testing between L and cpc at the fitting
 
...If i have read and calculated correctly,those figures put the initial test,with no lamps,at 30 meg ohms,so hardly a stella score to start with.Although,perfectly acceptable. Can the OP give any details of construction,age and design of fitting?
 
...If i have read and calculated correctly,those figures put the initial test,with no lamps,at 30 meg ohms,so hardly a stella score to start with.Although,perfectly acceptable. Can the OP give any details of construction,age and design of fitting?

Is is new fitting with all the lampholders wired seperatly back to the centre rose in 3 core flex. My question is why is there reading from live to earth through a new 52 w halogen type lamp. Am I not making myself clear or does nobody on here know the answer if that is the case I will endeavour to explore other avenues instead. Thankyou
 
Is is new fitting with all the lampholders wired seperatly back to the centre rose in 3 core flex. My question is why is there reading from live to earth through a new 52 w halogen type lamp. Am I not making myself clear or does nobody on here know the answer if that is the case I will endeavour to explore other avenues instead. Thankyou

What are the Earthing arrangements and was the Neutral still connected at the CU?
 
It sounds like the insulation in the lamp caps is poor, between the contact pips and the metal cap itself. This is not uncommon, I have had lamp caps read lower than the whole of the rest of the installation combined. If the lamps have been on, and hence warm, for a while, it probably isn't going to get any higher. But it doesn't sound like it's a problem, except that you have to take the lamps out to get a realistic test result on the wiring.
 
Last edited:
Is is new fitting with all the lampholders wired seperatly back to the centre rose in 3 core flex. My question is why is there reading from live to earth through a new 52 w halogen type lamp. Am I not making myself clear or does nobody on here know the answer if that is the case I will endeavour to explore other avenues instead. Thankyou
Whilst cruising down that avenue,swing in to Lucien street,near thank you close...:icon12:
 
Thanks Lucian. The readings are just through the lamp not the installation wiring so the earthing arrangement is irrelevant in this case.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Insulation resistance on candle 52w candle lamps new halogen type
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
ojbor,
Last reply from
ojbor,
Replies
21
Views
3,495

Advert

Back
Top