am now working on a property ( installing a second shower)

due to the load change . 2 x 8.5 kw showers = 74 A

And the main income only being 63A main fuse , 16mm tails. I need these upgraded .

Do i need western power + the suppliers out to do both sides ? ( ie after /before the meter ? )

Many thanks
 
Bet if you put a clamp on those showers, they won't be pulling 8.5 KW. For some reason, manufacturers are always a little over optimistic on the actual ratings!! lol!!
 
Bet if you put a clamp on those showers, they won't be pulling 8.5 KW. For some reason, manufacturers are always a little over optimistic on the actual ratings!! lol!!

I fully agree with you . I clamped one a while ago and was pulling 21A ,

However due to the design procedure we must follow i guess we should upgrade it yeah ?
 
However due to the design procedure we must follow i guess we should upgrade it yeah ?


Are there other loads.cooker,heaters etc,then as an alternative you could have only one running at a time,use a changeover switch or even fit a contactor and current sensing relay
 
Just to update.

Western power come out and despite the labels saying 60Amp fuse there was an 80 inside. !!!
they also left the tails @ 16mm......
 
Really ?...huh

I was to the understanding that 60amp for 16mm
And 80amp for 25mm

But you learn summat new everyday:-)
 
I was looking online a while ago and found a dual shower consumer unit. Can't remember where right now but I'm sure you ran one feed then connected the two shower loads and it would only allow one to work, good idea IMO don't think it was that expensive either 40/50 quid.....
 
I called DNO about a house I looked at once and needed change from 60 Amp to 100A,
Long story but they told me yes you can change it yourself if you are competent but best ring your local DNO to verify.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
main fuse/ tails upgrade
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
daiplayer,
Last reply from
Engineer54,
Replies
13
Views
3,485

Advert

Back
Top