Hi all was just looking to know does anyone know the max Zs for a
250-400 amp MCCB I can't find it anywhere in BS7671
250-400 amp MCCB I can't find it anywhere in BS7671
Try this as a start
http://www.terasaki.co.uk/PL0809_Lo_Res.pdf
By adjusting the settings you can set up both the thermal and magnetic trip. Knowing the maximum tripping current in each case will give you the approximate maximum impedance allowable.
This is just one site, found within 2 minutes. There's so much information out there.
Maximum fault current will be the same as a type C or 3 mcb (10x) but as with mcb manufactures, could be less. Unless of course it has an adjustable maximum tripping current facility.