Discuss N/E fault RCD not tripping ?? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
34
Hi all

can anyone give me the logic why the RCD wouldn’t trip on a neutral/earth fault. Testing a extension where they have added in 5 additional sockets to the upstairs ring had been powered up and nothing tripping with household appliances plugged in and working. Carrying out IR tests to find had dead short on one leg of the neutral and earth between 2 sockets but there was no issue of tripping ? RCD checks out ok with test button and RCD tests. Have disconnected this leg and then fitted fuse spur off the ring to carry the additional sockets now as to late to add in additional cable, so extension spurred off ring using fuse spur. Would it be the case that it had seized a bit RCD or that its connected to a TNCS system?? Replies much appreciated ?
 
it has been known for a N-E fault to inhibit the RCD from tripping, even on the test button. don't know the theory behind it, but i have seen it a couple of times.
 
Aww ok thanks for the reply ?. Had also a couple of other issues never seen before.

Trying to carry out Zs test on upstairs lights and found that it would carry out test as error code of >65 fre. Looked at the manuals and states supply frequency to high for test. So I disconnected the dimmer switch and managed to carry out test. Seems the dimmer is causing the frequency issue but don’t know why this would be as should be rated for 50hz ?

another issue think I know the issue on this one though IR test on socket circuit live to earth dead short. Join live and neutral together test down to earth >999mega ohms. Thinking with me going live to earth IR test travelling though USB ports on the sockets ? I noticed behind a cabinet was causing reading to be dead short. This is the only reason I can think of as unable to switch off USB ports ?
 
If you know there are usb sockets in the circuit, testing N-E insulation is a bad idea.
you can't say there is a dead short if testing with an insulation resistance tester.

I would only consider something to be a dead short if measured below 1 ohm.
 
Hi yeah I tested live to earth but coming up 0.00mega ohm but link neutral and live together then test then all clear >999 mega ohm so it’s like I’m testing through the USB when doing live to earth on the IR tests ?
 
Hi yeah I tested live to earth but coming up 0.00mega ohm but link neutral and live together then test then all clear >999 mega ohm so it’s like I’m testing through the USB when doing live to earth on the IR tests ?
If your neutral is disconnected from the neutral bar you should not get zero as your linked neutral/line to earth was clear.
 
Sorry I may not have followed things here fully, but if you are reading zero N - E but everything works etc then I’m thinking perhaps you’re recording the excellent N - E connection at the cutout?
 
But regarding the USB sockets. If I have not disconnected the neutrals from neutral bar and tested between live and earth and I am getting low reading basically zero near enough, this should be because the USB points are bringing the reading down as I will be going through the earth and being TNCS will be linked to neutral so will be testing the USB point. As when I link out live and neutrals at the consumer unit and go to a socket then test live to earth insulation resistance it comes out clear. >999mega ohms. Now if that was a damaged cable that would be picked up, does that make sense ?
 
But regarding the USB sockets. If I have not disconnected the neutrals from neutral bar and tested between live and earth and I am getting low reading basically zero near enough, this should be because the USB points are bringing the reading down as I will be going through the earth and being TNCS will be linked to neutral so will be testing the USB point. As when I link out live and neutrals at the consumer unit and go to a socket then test live to earth insulation resistance it comes out clear. >999mega ohms. Now if that was a damaged cable that would be picked up, does that make sense ?
What voltage are you doing insulation resistance test?
 
On both tests at 250v and 500v. I tested live to earth at 250volt seen that it was very low near enough zero, now this has been connected to a RCD and MCB for years this circuit. So I then joined live and neutrals together at consumer unit then tested live to earth IR test at nearest socket comes up >999mega ohms. So I am thinking I’m testing through the USB points when carrying out live to earth only with neutrals still connected to N bar ?? That make sense
 

Reply to N/E fault RCD not tripping ?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
275
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
543
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
388
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
720
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock