O
Octopus
All
Started on a rather large PIR this afternoon and have noticed the following so for:
1. Smoke alarm positioned over stairs
2. Some downlights completely covered in loft insulation
3. 13A socket in loft on lighting circuit
Was thinking about coding them 4, 2, 2
Your thoughts?
Where's the reg on smokes over stairs?...in order to be a code 4 it has to be a regulation in the BRB....may be I've got this one wrong.
13 amp socket on lighting circuit would be a code 4 from me, wouldn't be considered potentially dangerous as it'd trip out at 6 amps. Was possibly installed for a tv amp at a guess.
This was the one I was really pondering over. Yes its for a TV aerial amp
Socket on lighting cuircuit not even a Code 4 - doesn't break any rules. Could cause MCB to trip if he plugs his hair dryer in, but thats not dangerous.
Smoke detector over the stairs, only an issue if its difficult to change the battery, if its got a battery that is.
Ok, the last fault I found was a break in the CPC ring for the kitchen/breakfast room.
Today I found some time to go back and see if I could find it and I can "tell" that the CPC is not continuous between 2 sockets. Code 2 IMHO
FYI at the "furthest" socket before the break the EFLI and RCD values are OK
So how should I fix it without ripping open the walls and ceiling? I could go back out of the box, and run 2.5 T&E in conduit down the side of the house, in through the garage and down the back wall of the garage to the rear of the 2nd socket.
Anyone got any brighter ideas?
I'm off on hols this Saturday for a well earned break and want to put a suggestion to the owner before I go!
Split ring into 2 x 20A radials, making sure you disconnect all the ends of the branch where the CPC has broken. Would also pay to label in the box why you have done this.
Thought about this but radial would be the fridge and 1 double socket, and the other would be, the micowave, the kettle, the toaster, the dishwasher, the wine cooler .......
Hence why my plan is to rerun a cable to reinstate the ring.
Nice thought though!
PIR Codes - opinions please
Octopus,
Octopus,