There are 3 types of circuit faults;
Short circuit - A direct connection between any of the live conductors(L1,L2,L3 and Neutral)
Earth leakage - abnormal current on the earth conductor(Not sure if this is the best way to describe it)
Overload - too much current on an otherwise electrically sound circuit
Different Protective devices protect the circuit(And you) from one or more of these types of faults.
RCD(Residual Current Device) detects differences between the conductors and if for any reason the neutral comes back with less current then it should(Through the CPC) at a maximum of
30mA but a good RCD usually trips around 20mA a magnetic field within the device collapses operating(Tripping) the device. disconnecting the supply. This only protects against Earth leakage faults.
MCB(Miniature Circuit breaker) although now should be just called a
Circuit Breaker(CB) technically. Works by either Thermally using two dissimilar metals(Called a bimetallic strip) where one expands at a different temperature from one another causing it to bend therefore tripping the device or magnetically protects against overload AND short circuits
On the left is the thermal and the right being magnetic
MCCB(Moulded Case Circuit Breaker) like an CB but can be adjusted and fine tuned. these protect against all three faults
RCBO(Residual Current Circuit Breaker) a combination of an RCD and a CB. Protecting against all three faults and are quite costly
Reiterated what's already been posted but I hope but a different perceptive on it and helped you to understand more
I'm not expert on this so if someone could correct me where ever i may have been wrong that'd be great :lol: