Just move the sockets to wherever they need to go.Hi, I’m at a job on a grade 2 listed property with 5 different single phase distribution boards, the client wants sockets moved to new locations however the circuit I’m working on has a 32a rcbo but no SPD, all other circuits have to protection either. Any advice?
Thanks
More so regarding certification…?Just move the sockets to wherever they need to go.
You're making an alteration to an existing circuit, and I assume not in a special location.More so regarding certification…?
Thanks for the reply, it was just that no other circuit on this specific db had any form of protection bar the mcb itself, seems over the top to have to replace a board and add an spd etc for the sake of moving a few sockets. ThanksIf you want to be completely to the book you can advise them that adding SPD would be normal now, but they can chose to decline it. Of course, it would be worth checking first that they do not have any history of lightning-related damage.
ThanksI think check the regs. If I am reading you right I think you are getting at the need (?) for SPD which if it is domestic there is no particular part of the regs which insists on it. On the cert I would be inclined to note SPD was offered and the client has declined as you might. I presume you have discussed this with them?
Ah @pc1966 just pipped me there.
yes but the circuit is the only one in the db on an rcbo and no spd so wasn’t sure the take on completing a minor works taking into account the state of the property’s old electricsYou're making an alteration to an existing circuit, and I assume not in a special location.
You're making an alteration to an existing circuit, and I assume not in a special location.
If there is a spare MCB slot you can add SPD in a small DIN box outside of an older DB if really needed.Thanks for the reply, it was just that no other circuit on this specific db had any form of protection bar the mcb itself, seems over the top to have to replace a board and add an spd etc for the sake of moving a few sockets. Thanks
RCD protection is far more important, so that is good to hear!Ps the circuit I’m working on has a 32a rcbo
![]()
If there is a spare MCB slot you can add SPD in a small DIN box outside of an older DB if really needed.
For better protection you can route the sub-main through the DIN box to the SPD and then to the DB, assuming the type of SPD is good to the supply protection (e.g. 100A fuse). Many of the cheaper SPD need an MCB in the 32A or so region for protection, but not all. For example the Axiom single-unit from Toolstation, etc, is good to a 100A fuse and only £20!
The line terminal will take (probably) 2 * 16mm but neutral won't, so it needs a box with a neutral bar if used in this manner.![]()
Axiom Type 2 Surge Protection Device SP+N (SPD)
• Single pole and neutral• Single module• Does not require MCB protection• DIN-rail mountable• Type 2, single phase, double pole, suitable for TN-S, TN-C-S and TT earthing• Suitable for use in Axiom consumer units• Complies with IEC 61643-11• Dimensions: 18 x 81 x 71mm• 1 year warrantyOver...www.toolstation.com
Also an external SPD need not match the DB brand as it is not fitting in to the busbar design, etc.
RCD protection is far more important, so that is good to hear!
If there is a spare MCB slot you can add SPD in a small DIN box outside of an older DB if really needed.
For better protection you can route the sub-main through the DIN box to the SPD and then to the DB, assuming the type of SPD is good to the supply protection (e.g. 100A fuse). Many of the cheaper SPD need an MCB in the 32A or so region for protection, but not all. For example the Axiom single-unit from Toolstation, etc, is good to a 100A fuse and only £20!
The line terminal will take (probably) 2 * 16mm but neutral won't, so it needs a box with a neutral bar if used in this manner.![]()
Axiom Type 2 Surge Protection Device SP+N (SPD)
• Single pole and neutral• Single module• Does not require MCB protection• DIN-rail mountable• Type 2, single phase, double pole, suitable for TN-S, TN-C-S and TT earthing• Suitable for use in Axiom consumer units• Complies with IEC 61643-11• Dimensions: 18 x 81 x 71mm• 1 year warrantyOver...www.toolstation.com
Also an external SPD need not match the DB brand as it is not fitting in to the busbar design, etc.
RCD protection is far more important, so that is good to hear!