Hi, I’m at a job on a grade 2 listed property with 5 different single phase distribution boards, the client wants sockets moved to new locations however the circuit I’m working on has a 32a rcbo but no SPD, all other circuits have to protection either. Any advice?

Thanks
 
Hi, I’m at a job on a grade 2 listed property with 5 different single phase distribution boards, the client wants sockets moved to new locations however the circuit I’m working on has a 32a rcbo but no SPD, all other circuits have to protection either. Any advice?

Thanks
Just move the sockets to wherever they need to go.
 
If you want to be completely to the book you can advise them that adding SPD would be normal now, but they can chose to decline it. Of course, it would be worth checking first that they do not have any history of lightning-related damage.
 
I think check the regs. If I am reading you right I think you are getting at the need (?) for SPD which if it is domestic there is no particular part of the regs which insists on it. On the cert I would be inclined to note SPD was offered and the client has declined as you might. I presume you have discussed this with them?
Ah @pc1966 just pipped me there.
 
If you want to be completely to the book you can advise them that adding SPD would be normal now, but they can chose to decline it. Of course, it would be worth checking first that they do not have any history of lightning-related damage.
Thanks for the reply, it was just that no other circuit on this specific db had any form of protection bar the mcb itself, seems over the top to have to replace a board and add an spd etc for the sake of moving a few sockets. Thanks
Ps the circuit I’m working on has a 32a rcbo
👍
 
I think check the regs. If I am reading you right I think you are getting at the need (?) for SPD which if it is domestic there is no particular part of the regs which insists on it. On the cert I would be inclined to note SPD was offered and the client has declined as you might. I presume you have discussed this with them?
Ah @pc1966 just pipped me there.
Thanks
You're making an alteration to an existing circuit, and I assume not in a special location.
yes but the circuit is the only one in the db on an rcbo and no spd so wasn’t sure the take on completing a minor works taking into account the state of the property’s old electrics
You're making an alteration to an existing circuit, and I assume not in a special location.
 
Thanks for the reply, it was just that no other circuit on this specific db had any form of protection bar the mcb itself, seems over the top to have to replace a board and add an spd etc for the sake of moving a few sockets. Thanks
If there is a spare MCB slot you can add SPD in a small DIN box outside of an older DB if really needed.

For better protection you can route the sub-main through the DIN box to the SPD and then to the DB, assuming the type of SPD is good to the supply protection (e.g. 100A fuse). Many of the cheaper SPD need an MCB in the 32A or so region for protection, but not all. For example the Axiom single-unit from Toolstation, etc, is good to a 100A fuse and only £20!

The line terminal will take (probably) 2 * 16mm but neutral won't, so it needs a box with a neutral bar if used in this manner.

Also an external SPD need not match the DB brand as it is not fitting in to the busbar design, etc.
Ps the circuit I’m working on has a 32a rcbo
👍
RCD protection is far more important, so that is good to hear!
 
If there is a spare MCB slot you can add SPD in a small DIN box outside of an older DB if really needed.

For better protection you can route the sub-main through the DIN box to the SPD and then to the DB, assuming the type of SPD is good to the supply protection (e.g. 100A fuse). Many of the cheaper SPD need an MCB in the 32A or so region for protection, but not all. For example the Axiom single-unit from Toolstation, etc, is good to a 100A fuse and only £20!

The line terminal will take (probably) 2 * 16mm but neutral won't, so it needs a box with a neutral bar if used in this manner.

Also an external SPD need not match the DB brand as it is not fitting in to the busbar design, etc.

RCD protection is far more important, so that is good to hear!

Thanks again for the reply, I think the point I’m getting at is, does there have to be an spd when adding to the circuit or does the spd rule apply for just new circuits/ changing the db
Thanks
 
Last edited by a moderator:
If there is a spare MCB slot you can add SPD in a small DIN box outside of an older DB if really needed.

For better protection you can route the sub-main through the DIN box to the SPD and then to the DB, assuming the type of SPD is good to the supply protection (e.g. 100A fuse). Many of the cheaper SPD need an MCB in the 32A or so region for protection, but not all. For example the Axiom single-unit from Toolstation, etc, is good to a 100A fuse and only £20!

The line terminal will take (probably) 2 * 16mm but neutral won't, so it needs a box with a neutral bar if used in this manner.

Also an external SPD need not match the DB brand as it is not fitting in to the busbar design, etc.

RCD protection is far more important, so that is good to hear!

Thanks again!, what’s your take on completing a minor works certificate in this scenario given the client states they don’t want an spd fitted due to excessive costs for the job. Also the old state of the rest of the properties electrics.
Thanks
 
The requirement for SPD is covered by 443.4.1 and outside of the mandatory cases (i) to (iii) it has the allowed exception if the owner declares it is not required.

Of course that has to be informed consent, so if you offer it and they decide the extra cost is not justified of a reasonable basis such as no history of trouble, then you just keep a copy of their decision and note it on the certificate that the client declined SPD.

For a new install I would always fit SPD as extra cost is now very small compared to the total cost of, say, a CU change.
 

Reply to SPD on old db in house with 5 boards all other circuits no protectiob in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
493
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
I’m just finishing my L2 2365 at college in the evenings and plan to do the L3 2365 with the same college as an evening course. However I would...
Replies
0
Views
238
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock