matt1386

Morning guys, im looking for a bit of advice please

A friend of mine has rang me asking if I could have a look and see if I know why their lighting circuit keeps tripping

They know my situation ( a trainee ) and ive explained I will have a visual look and see if I can notice anything obvious, but anything more than that they will have to get somebody in

There have been no problems on the circuit until yesterday and no light fittings have been changed

They said it would stay on for a couple of minutes, and then knock off again

I went round yesterday, flicked it back on and it held while I was there ( around 20 minutes ) but by the time they got home it had tripped again

Could somebody please tell me what basic inspections I can carry out please ? ( I dont own any test equipment and to be honest dont know how to use the equipment correctly so thats out the window)

I was thinking of checking for loose terminations on all fittings and switches, any outside lights that could be on the corcuit and full of water etc.. Any blown bulbs... Anything else guys ?

Im just not sure why its taking a different amount of time to trip the breaker ?

Thanks very much :-)
 
  • Like
Reactions: 1 person
I guess you could isolate the circuit using the MCB and visually check everything. I'd be looking for stuff that's been added like outside lights and checking areas where any work has been done such as hanging pictures ar anything involving a drill or masonry nails. Without test equipment your options are pretty limited.
 
  • Like
Reactions: 1 person
Sounds like the thermal trip in the MCB is going , once it reaches its tripping temp it lets go. What size MCB is it and whats the total load on the circuit?
 
Cheers for replies guys, just been over for a quick look as i had to get back home for somebody coming

The breaker is a GET B6, consumer unit is located in kitchen

breaker trips even with all lights off after a few minutes

The only lights that work in the house when the breaker is holding are the kitchen ones ( there are 2, and both the closest to the C.U, no power going to any other ones at the pendant or switch

At one point i turned the kitchen lights on, and the lamps were very dim with a slight buzzing coming from C.U

There is only 1 cable going to the fittings

7 pendants overall in the house

Checked all connections at switches, pendants and C.U and all seemed fine

Any ideas guys ?

Thanks very much
 
(Warning! Trainee answer!)

Clarification: you say, "The only lights that work in the house when the breaker is holding are the kitchen ones (there are 2, and both the closest to the C.U, no power going to any other ones at the pendant or switch)."

Do you mean that there is only one lighting circuit? (like my old house)? And the two lights nearest the CU (in the kitchen) are sort of working, but a bit dim, and that the other ones (further from the CU) don't work?

If this is correct, then it sounds like either the L or N has come loose in a junction box/pendant fitting that goes on to supply the other lights in the circuit. It is wafting around, and might be lightly resting on the other line conductor (so if L, then resting on N). Or it could be water damage leading to similar, but if the other lights further down the circuit aren't working at all then it sounds like summat's actually come loose.

If you're able to safely isolate, prove dead and somehow lock off, then you could start taking pendants/JBs apart to have a nosey. Ah, you've already looked in the pendants. Junction box under upstairs floorboards somewhere?
 
Last edited:
Hiya Steve, cheers for the reply mate,

Yes just the one lighting circuit covering the whole house

The kitchen lights actually worked fine when the breaker was holding, apart from once when they came on very dim with a slight crackling coming from C.U, every other time they were fine until mcb tripped

And yes, no power at all going to any of the other lights

I actually told them I thought it could be a problem with a JB under the floor, but said I would get some advice on here first before doing anything else

Thanks mate
 
Last edited by a moderator:
Have you checked the MCB is sitting on the bus bar properly and the connection is sufficiently tight. :)

Check the connections in the CU also.
 
  • Like
Reactions: 2 people
Yes Simon, thats the first thing I checked mate were all the connections in the mcb, give them all a pull and all were tight, also tried nipping them up with screwdriver and they were all nice and tight

At college I havent got onto the installation side of things yet, im still on the science part so im very limited on what I know

But, if i was to link out at the consumer unit on that circuit, and then go round each pendant checking for continuity, would that then give me an idea of where the break could be ( if there is a break obviously ) ?

I do have a voltage tester which does continuity

Im just trying to save the old lass a bit of cash thats all, but obviously if its something that im not competent to do at this stage then she will have to get somebody else in who is

cheers :-)
 
You would really benefit from having a multifunction tester and a wondering lead as this would give you accurate readings.

Have you considered the mcb may be knackered? Try changing it possibly.
 
Your right mate, I just cant justify the cost for it to be sat there as at the moment i dont have a clue how to use most of the functions on there haha !

Ill get a replacement breaker and try that then first

cheers buddy !
 
Eh up again :)

Blimey this is the blind leading the blind here, isn't it?!? (no offense to either of you, more having a dig at myself really!). I bet the experienced guys are having a giggle at this, no doubt shaking their heads...

Anyway, aside from finding the fault... sounds like this old lass is a friend of yours. She's only got one lighting circuit in the house, and at the moment it doesn't work. It'll be dark in about 6 hours. Has she got enough lamps and stuff plugged into sockets that she'll be safely able to get around the house tonight without tripping over any extension leads? (You've probably already thought about this, sorry if it's obvious!).

In terms of fault finding - not done this on the course yet, and my previous experience is all extra low voltage stuff. Dead tests are safer than live tests, so if you can completely isolate the circuit, and have got a continuity tester and a way of making a wander lead, then yep you could use that to find where the fault is, even if you can't get to it!

The "two lights closest to the CU work, the other ones don't" is a gift of a clue. Use this information, and continuity tests if you can, to find it. :)
 
Last edited:
  • Like
Reactions: 2 people
Yeah I agree steve lol, the only way to solve the issue is to be there on site armed with the right tools etc. :)

Its guess work otherwise in all fairness.
 
my first check would be to ensure that the MCB is sitting correctly on the busbar. very common problem is that the busbar sits behind the terminal, esp. with wylex. also swap the MCB. ( simin said this in previous posts ). then start looking for circuit faults.
 
  • Like
Reactions: 5 people
I think this is interesting for trainees to read and work out or try understand haha. And telectrix is an old helpful boy he rarely shakes his head and is quite helpful isnt he. :) I learn loads off you lot!!! Owt i dont understand il look up or ask :)
 
  • Like
Reactions: 1 person
Drum of singles and continuity tester is what I would use to check for loose connection.

First thing though is there one or more cables at each fitting?

If there is only one then there is a probably a jb somewhere
 
  • Like
Reactions: 2 people
Cheers shanky, only 1 cable at each fitting mate which suggest to me a JB between fittings as you say

Ive taken on board what you have all said and will give it another go in the morning, I WILL fix the problem lol !

Only thing bothering me was the one time I turned the switch on and the lights were dim, with a crackling coming from C.U which to me I would have said loose connection but I checked and the cables were tight

Steve, yes mate, ive given her a a few lamps just for at night, shes plenty of light in there :-)

Cheers guys, this is what the trainee section is all about ! :D
 
  • Like
Reactions: 1 person
Good stuff, mate. You'll sort it :)
 
Just to be sure you have checked that all the connections are tight in the cu and not just the circuit you are faultfinding on?

As you have said crackling could indicate a loose or poor electrical connection.

My dad had a spark put in a board for an outside music studio in and the idiot didnt tighten the breaker on to the bus bar , anyway the busbur turned black and the cu nearly caught fire.

Seriously visually look to see the breakers are sat on the busbar correctly and as tel said not placed on it but behind the mcb terminal.
 
  • Like
Reactions: 2 people
I did check mate, but I will definitely check again in the morning, ill go and grab a new mcb to try aswell so will make sure everything is fitted and terminated correctly when I go back

Cheers Simon and everyone else, great advice in this section as always !
 
  • Like
Reactions: 2 people
Pretty much as tel says really, if you have access to the loft you could look for jbs with loose terminations and any obvious signs of damage if you dont know how to use a MFT. Obviously isolating first and proving dead with your voltage tester!
But i admire your opening post and honesty to say that your a trainee and have no idea how to use a MFT. Some of the keyboard gangsters on here will say you should not be doing anything without supervision blah blah blah but you said yourself if its out of your depth then you will leave it to a competent sparks.
This is how you learn and it has got your brain thinking and hope you find the fault mate !!
 
  • Like
Reactions: 4 people
If you had lights coming on dimly and there was a crackling at the CU then it's very highly likely there's a poor connection in the CU somewhere.
 
  • Like
Reactions: 1 person
Alright Matt, lets get the old lass sorted out. I'll pop over on Friday with everything you need to get the perfect end result for her. Well it is Good Friday so lets do something good lol. And yes it is free of charge.

This is a good little fault finding exercise for you, seems like you are looking in the correct direction already with the help from all the other trainee's (which I am very impressed with BTW, well done, I love it).

Sort a time out with your "customer" for Friday, (about 9:30 - 11:00 suits me. Well it is a bit of a drive..... kind of) Matt you have my number so give me a call/text or PM and we will go round and fix it. Simple has that really. I'll show you my way of step by step fault finding, same as what has been posted up already but no-one has mention a "spider JB" yet? I think it is a bit more than that but it will be working by the time we leave the house Matt, that I am sure off :wink:
 
  • Like
Reactions: 5 people
looks like i'll have to have a word with the pope. st.paul sounds good. :hurray:
 
  • Like
Reactions: 2 people
looks like i'll have to have a word with the pope. st.paul sounds good. :hurray:

And within the same hour as that post, I have been made a Moderator!!!!! Well, it's not quite Pope but it will do for now pmsl.

Whoops, am I allowed to say things like pmsl etc??? I'll have to go to the Mods section and look at the new rules that I am now under :rofl:


PS.... Nothing much will change about me.

Paul M
 
  • Like
Reactions: 4 people
paul a mod..... that's like putting heinrich himmler in charge of the synagogue, lol. :lipsrsealed2:
 
  • Like
Reactions: 2 people
Whoops, am I allowed to say things like pmsl etc??? I'll have to go to the Mods section and look at the new rules that I am now under :rofl:


PS.... Nothing much will change about me.

Paul M

Yes! :-)
 
Alright Matt, lets get the old lass sorted out. I'll pop over on Friday with everything you need to get the perfect end result for her. Well it is Good Friday so lets do something good lol. And yes it is free of charge.

This is a good little fault finding exercise for you, seems like you are looking in the correct direction already with the help from all the other trainee's (which I am very impressed with BTW, well done, I love it).

Sort a time out with your "customer" for Friday, (about 9:30 - 11:00 suits me. Well it is a bit of a drive..... kind of) Matt you have my number so give me a call/text or PM and we will go round and fix it. Simple has that really. I'll show you my way of step by step fault finding, same as what has been posted up already but no-one has mention a "spider JB" yet? I think it is a bit more than that but it will be working by the time we leave the house Matt, that I am sure off :wink:
Did you fettle it? :)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Tripping mcb - lighting circuit
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
29

Advert

Thread statistics

Created
matt1386,
Last reply from
Paul.M,
Replies
29
Views
445

Advert