Hi all,

I was looking at a CU today and couldn’t help noticing it had two supply cables. Does anyone know if this is a DNO loop system from one property to the next (I know the photo isn’t the best). The board is located near the entrance to the property and it is a semi detached house.


1AACCA73-2FC2-4844-B3C2-66B239ED4901.jpeg
 
almost certain to be loop in and out to next door.
 
  • Agree
Reactions: James
almost certain to be loop in and out to next door.

Thanks for your reply telectrix. I have not come across a incoming supply that looks like the one above before. How would one go about changing the CU in this circumstance without disconnecting the supply to the neighbours? Would it be necessary to contact the DNO before the work was undertaken?
 
if you pull the fuse, it will only disconnect that house. it will not affect next door. it's an oldish head though so either call DNO or (naughty) pull the Lout from out of the meter (live). then get seal fairy to reseal.
 
  • Like
Reactions: anth125 and DPG
Right, i understand; it cuts the main supply from going to and past the meter of that property but there is still a continuous supply to the next property even with the fuse pulled.

Is it common to find those bare conductors leading from the concentric cable into the earthing terminal on the service head
 
Gas meter is a bit close.

If that’s a smart meter, was an isolator not put in at the same time?
 
Is it common to find those bare conductors leading from the concentric cable into the earthing terminal on the service head
Not common but OK. The old head looks like it's been adapted with a newish incomer (and loop on). It's not very common, either, to have an enclosed main earth block, these days. It's getting on a bit but looks in good nick, except for the green main earth looking undersized. Is the g/y bonding conductor 10mm?
 
Not common but OK. The old head looks like it's been adapted with a newish incomer (and loop on). It's not very common, either, to have an enclosed main earth block, these days. It's getting on a bit but looks in good nick, except for the green main earth looking undersized. Is the g/y bonding conductor 10mm?

I would have to check the size of the g/y earth however, I agree that the main earthing conductor is undersized and looks like a 6mm
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
What is this?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
8

Thread Tags

Advert

Thread statistics

Created
anth125,
Last reply from
anth125,
Replies
8
Views
1,912

Advert