Hi all. The title is a slight red-herring to provoke a response....

Looking through previous threads here and elsewhere tells me that the formula in the title just isn't true - that you cannot just measure Zs at a socket outlet (live test) and subtract a measured Ze to get an R1+R2 value for your minor works certificate.

Fair enough - I thought - Ze requires the earthing conductor to be temporarily removed, parallel paths etc - so I can see why it wouldn't work....

So - it seems odd then that my MFT seems to encourage doing just exactly that - entering a Zref value (Ze or Zbd) then doing your live Zs as normal and it will actually subtract the Zref and give an "R1+R2".

Am I missing something here?
I don't get it?
 
My megger ELI meter has the same function. Just because it's there doesn't mean you have to use it.
 
From what I've read, Zs minus Zdb will sometimes give you an accurate R1+R2 (provided that there are no parallel paths), but it's really bad practice because you can't guarantee that you're getting true readings.
 
My MFT has the same function, it seems like it could be used as a quick reference whilst carrying out testing to check that a measured Zs correlates to the R1+R2 previously measured.
 
  • Like
  • Agree
Reactions: DPG and Dave OCD
If your MFT is encouraging you to do anything, you should stop talking to it and get a holiday.

Great idea - but can I take it with me?
 
  • Funny
Reactions: Zdb
My MFT has the same function, it seems like it could be used as a quick reference whilst carrying out testing to check that a measured Zs correlates to the R1+R2 previously measured.
The 3 things are slightly different so the best method is to perform 3 measurements, IMHO :)
 
  • Creative
Reactions: 1 person

Thanks for the replies. Great stuff.

I'll just carry on as I think I should - if I add a socket to a Ring Final then I'll go for the full cross connection R1+R2 test (and Ze/polarity). Remove the doubt. It takes a while though. It's just that background feeling of not wanting to disconnect the circuit from the consumer unit unless I have to. But that's what I'll do!
 
Thanks for the replies. Great stuff.

I'll just carry on as I think I should - if I add a socket to a Ring Final then I'll go for the full cross connection R1+R2 test (and Ze/polarity). Remove the doubt. It takes a while though. It's just that background feeling of not wanting to disconnect the circuit from the consumer unit unless I have to. But that's what I'll do!

Nothing stopping you dead testing at an available socket.
 
  • Like
Reactions: GlenTavener
Thanks for the replies. Great stuff.

I'll just carry on as I think I should - if I add a socket to a Ring Final then I'll go for the full cross connection R1+R2 test (and Ze/polarity). Remove the doubt. It takes a while though. It's just that background feeling of not wanting to disconnect the circuit from the consumer unit unless I have to. But that's what I'll do!

Marcus you don't have to disconnect at the DB to do the cross connection/figure of 8 test - just do it at a socket with both ring legs in it.
 
It's just that background feeling of not wanting to disconnect the circuit from the consumer unit unless I have to

If you're extending the ring and not adding a spur you could always do end to end tests at the socket outlet and calculate your R1+R2. That way you don't have to disconnect anything at the D.B.

I think it's okay to use this method?
 
Andy beat me to it - but I explained it better. :D
 
  • Agree
Reactions: Andy78
If you're extending the ring and not adding a spur you could always do end to end tests at the socket outlet and calculate your R1+R2. That way you don't have to disconnect anything at the D.B.

I think it's okay to use this method?

No you have to do the cross connecting as well to check it's actually a ring , then each socket should have pretty much the same reading apart from spurs which will obviously be higher.
 
Marcus you don't have to disconnect at the DB to do the cross connection/figure of 8 test - just do it at a socket with both ring legs in it.
Dave - sometimes I can't see the wood for the trees. Brilliant and simple at the same time. Thankyou. To me it makes sense to cross connect at the last new socket going in - and test at the consumer unit. I could always do a quick live Zs test on this last socket once it's in to ensure 'all is good'.
 
  • Like
Reactions: Dave OCD
Happy to help mate. :)
 
op have got a onsite guide!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Sheffield
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Zs-Ze = R1+R2 - doesn't it?!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
Marcus Vaughan,
Last reply from
buzzlightyear,
Replies
22
Views
10,982

Advert