Discuss Fault Find - advice please! in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
15
Team - I'm after some help on a fault find that I was at this week and to work out if there's something obvious that I've forgotten, overlooked. I've only been working as a spark for a couple of years, done my city & guilds 2365 - L2&3 and done my AM2, just wanting to finish my portfolio for my NVQ - (just ome back ground to get me out of the DIY forum).

Customer reports RCD trip on down stairs ring circuit, MK split load board, half RCD protected, and half isn't. After a lot of messing about working out what was and wasn't on the circuit, eventually removed all the loads (found a few hiding) and IR tests commence. RCD is a MK 80a - 3oma, fault appears to be intermittent but there is no issues when the down stairs ring is switched off - so I'm happy that is where the problem lies.

L-E 530 MΩ, N-E 383 MΩ, L-N >999 MΩ- I measured this at the board and at a socket on the down stairs ring.

There is a brake in the ring on the line conductor, which I think is a historic problem, contained within one of the spider web of junction boxes underneath floorboards upstairs, which are underneath a very expensive floor. I have explained the need to trace it. – however the customer has sold the house to a developer who is only a couple of months away from levelling the place.

RCD test - trips @ 1/2 rate when testing on that circuit. So I disconnected the down stair ring and ramp test it from upstairs - trips @ 19ma. I thought it was a bit sensitive, so swapped it out for a new one. Same story, however the RCD holds now and does so for some time. 4 days in one instance.

But when the loads start to be plugged back in – The only thing I had in was the fridge freezer and the TV (which is in three way adapter thing) virgin media box. I’ve checked the fridge freezer cpc with a clamp meter on an extension lead – no issues, trips whilst I’m there. I take the freezer out and fridge and trips 5 mins later. The only thing in is the tv / media thing. Checked that with a clamp meter and no issues. I’ve left the client after a good few hours and I started to struggle to see the wood for the trees by this point. So I told him to take that out and slowly put things back in at 30 minute intervals – thinking could it be an intermittent fault with an appliance like a compressor on a fridge that isn’t constantly running?

So my questions are this – why would the rcd trip at half trip current on that circuit only, with no loads, despite good IR tests - is it still likely to be fixed wiring?

Could the TV / media thing have a component that is intermittently working and faulty? – When I suggested the tv he did say his son had had the back off and fitted his own speakers to it……. (my ears did ----- up at that)

Testing with a new megger mft 1711 by the way.

Anything I’ve forgotten – if it’s obvious – please don’t shoot me, it’s been a long day!
 
Last edited:
YOU COULD STARTBY TYPING IN A FONT AND SIZE THAT I CAN READ WITHOUT A MAGNIFYING GLASS.:D:D.
soz aboutthe caps.was rthe lock after givingmyreg.to the tollbridge so they could rob me a gain.
 
Team - I'm after some help on a fault find that I was at this week and to work out if there's something obvious that I've forgotten, overlooked. I've only been working as a spark for a couple of years, done my city & guilds 2365 - L2&3 and done my AM2, just wanting to finish my portfolio for my NVQ - (just ome back ground to get me out of the DIY forum).

Customer reports RCD trip on down stairs ring circuit, MK split load board, half RCD protected, and half isn't. After a lot of messing about working out what was and wasn't on the circuit, eventually removed all the loads (found a few hiding) and IR tests commence. RCD is a MK 80a - 3oma, fault appears to be intermittent but there is no issues when the down stairs ring is switched off - so I'm happy that is where the problem lies.

L-E 530 MΩ, N-E 383 MΩ, L-N >999 MΩ- I measured this at the board and at a socket on the down stairs ring.

There is a brake in the ring on the line conductor, which I think is a historic problem, contained within one of the spider web of junction boxes underneath floorboards upstairs, which are underneath a very expensive floor. I have explained the need to trace it. – however the customer has sold the house to a developer who is only a couple of months away from levelling the place.

RCD test - trips @ 1/2 rate when testing on that circuit. So I disconnected the down stair ring and ramp test it from upstairs - trips @ 19ma. I thought it was a bit sensitive, so swapped it out for a new one. Same story, however the RCD holds now and does so for some time. 4 days in one instance.

But when the loads start to be plugged back in – The only thing I had in was the fridge freezer and the TV (which is in three way adapter thing) virgin media box. I’ve checked the fridge freezer cpc with a clamp meter on an extension lead – no issues, trips whilst I’m there. I take the freezer out and fridge and trips 5 mins later. The only thing in is the tv / media thing. Checked that with a clamp meter and no issues. I’ve left the client after a good few hours and I started to struggle to see the wood for the trees by this point. So I told him to take that out and slowly put things back in at 30 minute intervals – thinking could it be an intermittent fault with an appliance like a compressor on a fridge that isn’t constantly running?

So my questions are this – why would the rcd trip at half trip current on that circuit only, with no loads, despite good IR tests - is it still likely to be fixed wiring?

Could the TV / media thing have a component that is intermittently working and faulty? – When I suggested the tv he did say his son had had the back off and fitted his own speakers to it……. (my ears did ***** up at that)

Testing with a new megger mft 1711 by the way.

Anything I’ve forgotten – if it’s obvious – please don’t shoot me, it’s been a long day!
Where did you ramp test the RCD?
 
I think the previous RCD was waiting to be replaced like you've done.
If the only thing connected is the T.V and it trips then it sounds like the likely culprit.
Is there is a break that cannot be found then do we split into two radials, tin hat on
 
Remember your ir tester does dc but the mains is ac, you could have a capacitive leak.
Try putting a meter on the (Edit): live conductors of the circuit to see what the normal leakage is and then connect the loads. Could just be an accumulation of leaky devices.
Edit sorry brain fart on which conductors the rcd measures:rolleyes:
 
Last edited:
I think the previous RCD was waiting to be replaced like you've done.
If the only thing connected is the T.V and it trips then it sounds like the likely culprit.
Is there is a break that cannot be found then do we split into two radials, tin hat on
Yep - that will be my next move, not ideal, but customer has sold the house and renting it off a developer until they complete on their new house. Thank you
 
RCD test - trips @ 1/2 rate when testing on that circuit. So I disconnected the down stair ring and ramp test it from upstairs - trips @ 19ma. I thought it was a bit sensitive, so swapped it out for a new one. Same story, however the RCD holds now and does so for some time. 4 days in one instance.

freezer cpc with a clamp meter on an extension lead – Checked that with a clamp meter and no issues.
So my questions are this – why would the rcd trip at half trip current on that circuit only, with no loads, despite good IR tests - is it still likely to be fixed wiring?

You should test the RCD at the RCD with outgoing circuits disconnected not from remote points on a circuit, especially not a circuit known to have a fault.

Are you using a standard clamp meter or one designed to measure earth leakage/very small currents? An earth leakage clamp meter should be put around all live conductors to measure earth leakage rather than measuring the earth current.

The RCD would trip at half current when tested in circuit because the earth leakage on the circuit will bias it to trip, this is why you don’t test RCDs this way.
 
Why? The RCD only failed the test when the test was carried out incorrectly, it would be better to replace the person doing the testing than the RCD.
Sorry Dave I've tested RCD's in both ways you've described. But testing the RCD remotely was exactly how I was shown to do it both on my city & guilds and AM2.

I appreciate it may seem obvious to you not to test it on a faulty circuit, but I thought the fault had been rectified.

My question was posted to learn, get some more knowledge, not to be insulted. If you haven't got anything constructive to add, please don't bother. I know I'm not the best sparky in the world, but no-one has the monopoly on good ideas just yet, so I thought I'd try and learn something and post on a forum designed to help people, not shout about how great they are.
 
if he's selling off to a developer,just leave a few live ends lying round to remind him to get s competent spark in to do his new installation.

Helpful. Thanks for the input.

I read this forum most weeks - I've learnt a lot from other people's questions, but time and time again I see people asking for help just get slated. (DIY'ers aside)

Genuinely, what is the point........... another keen user of the forum lost.
 
Helpful. Thanks for the input.

I read this forum most weeks - I've learnt a lot from other people's questions, but time and time again I see people asking for help just get slated. (DIY'ers aside)

Genuinely, what is the point........... another keen user of the forum lost.
seems like you can't accept a bit of banter. if so, plumbing might be a better career.
 
seems like you can't accept a bit of banter. if so, plumbing might be a better career.
Mate it's difficult to grasp the tone in text and when the last few posts were critical and personal rather than helpful I hope you can see why I may have misinterpreted your post, if it was just banter, then my apologies for flying off the handle.
 
Hi Mike - once there are circuit faults you will only get a clear result if you do the RCD test with circuits removed as per #22. Then if RCD tripped at 15mA or less it's out of spec, as it should not trip at 15mA. Since it's not resolved, I would look for N-E fault in any circuit of the installation. Good hunting :)
 
Hi Mike - once there are circuit faults you will only get a clear result if you do the RCD test with circuits removed as per #22. Then if RCD tripped at 15mA or less it's out of spec, as it should not trip at 15mA. Since it's not resolved, I would look for N-E fault in any circuit of the installation. Good hunting :)
Really appreciate that, thanks
 
Is the downstairs a solid floor or floorboards? You say the downstairs sockets are a ring.Does each socket downstairs have at least 2 twins in each socket or is the ring upstairs via joint boxes and just legs run down to each socket(if it's solid floors)?

If the floor is floorboards then it should be wired from underneath.In which case you need to start taking off sockets and disconnecting each leg of the ring and testing back to the mains.If that leg is totally clear then move onto the next leg and disconnect and test.My guess is the lack of continuity on the lives is probably where the fault is also.
Don't forget that just because the insulation resistance is reading clear on your meter doesn't mean that there is an arc somewhere within the ring and your tester isn't powerful enough to bridge the gap.If the fault is in the upstairs joint boxes then your going to have a hard time finding it without lifting the floor.

Good luck!
 
When testing your IR to earth did you include the earth bar, i.e. were the cpcs connected to the earth bar at the time of test or were they disconnected cables.
If they were disconnected cables then there maybe a fault from a live conductor to a different earthed part, so a repeat IR test from the live conductors to the earth bar may give a faulty result.
Presumably because the RCD is almost holding at times the fault sound like a progressive fault i.e. it has been getting worse and worse until it just starts to trip the RCD. This would then tend to indicate something like slow water/moisture build up or a partial breakdown of an electronic circuit.
Just some thoughts.
 
I know I left after my first x
Unwarranted of course with no explanation as to why everyone does the same jobs ther own tried and tested way but finding out how others do it is sometimes helpful and can help others still not sure and apprehensive
 
Last edited:
Hi Mike - once there are circuit faults you will only get a clear result if you do the RCD test with circuits removed as per #22. Then if RCD tripped at 15mA or less it's out of spec, as it should not trip at 15mA. Since it's not resolved, I would look for N-E fault in any circuit of the installation. Good hunting :)
Really appreciate that, thanks
Is the downstairs a solid floor or floorboards? You say the downstairs sockets are a ring.Does each socket downstairs have at least 2 twins in each socket or is the ring upstairs via joint boxes and just legs run down to each socket(if it's solid floors)?

If the floor is floorboards then it should be wired from underneath.In which case you need to start taking off sockets and disconnecting each leg of the ring and testing back to the mains.If that leg is totally clear then move onto the next leg and disconnect and test.My guess is the lack of continuity on the lives is probably where the fault is also.
Don't forget that just because the insulation resistance is reading clear on your meter doesn't mean that there is an arc somewhere within the ring and your tester isn't powerful enough to bridge the gap.If the fault is in the upstairs joint boxes then your going to have a hard time finding it without lifting the floor.

Good luck!
Thanks Bob - my thoughts exactly. It's lift the floor or chase my tail around a bit more. I appreciate the thoughts on the arcing though. I had split the ring and tested back towards the board, but IR tests came back satisfactory. But I think your right, the brake in the line conductor is likely to be the location of both faults.
 
When testing your IR to earth did you include the earth bar, i.e. were the cpcs connected to the earth bar at the time of test or were they disconnected cables.
If they were disconnected cables then there maybe a fault from a live conductor to a different earthed part, so a repeat IR test from the live conductors to the earth bar may give a faulty result.
Presumably because the RCD is almost holding at times the fault sound like a progressive fault i.e. it has been getting worse and worse until it just starts to trip the RCD. This would then tend to indicate something like slow water/moisture build up or a partial breakdown of an electronic circuit.
Just some thoughts.
Thanks Richard, just to answer your question, I did test with the earths connected. I took the neutrals out, but the earths were connected.

I thought the fault might be a component in an appliance that isn't running constantly like a fridge compressor or a heating element in the washing machine etc.

Really appreciate the feedback - thanks
 
Fault finding is all a process of steps, it takes a while to learn the shortcuts that can help speed things up. Forget all the leg pulling they’re just teasing, plus don’t take what you did in your am2 as gospel. They don’t like you working in live boards hence the rcd rest remotely, as a spark you will inevitably have to work on/in live boards.

Ramp the RCD at the board with loads connected/Not and note the difference, this is your leakage.

Next do a global IR with all circuits on(mcb not power) and slowly turn them off to find out which has the short.

Then it’s a process of halfing the circuit until you narrow it down, remember the leakage might be accumulative across multiple circuits.

Good luck
 
Thanks Richard, just to answer your question, I did test with the earths connected. I took the neutrals out, but the earths were connected.

I thought the fault might be a component in an appliance that isn't running constantly like a fridge compressor or a heating element in the washing machine etc.

Really appreciate the feedback - thanks
OK then it might be worth testing IR: line on your side to the other neutral bar, or if there are too many loads just between neutral bars with the RCDs out of circuit and MCBs On, main switch off, to see if there is a connection across circuits. This would allow some current to flow down a different path and trip the RCD, however if the circuits are all well separated and the other RCD is not tripping then this is less likely.
If the RCD is tripping with any load then it is likely to be a circuit issue rather than an appliance.
 

Reply to Fault Find - advice please! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Gone to look at a intermittent ground floor sockets fault today, the RCBO was tripping at random times with no pattern. Nailed down a...
Replies
11
Views
2K
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
383
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
861

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock