Just want other people's opinions on this

In a warehouse were 16amp sockets are used for conveyors only would these need to be installed with rcbo's or just an mcb?
 
2.5 swa ran in cable tray on a 16A mcb and will be labelled conveyors only ,this is an exsisting installation iv come across as adding another 2 outlets to this circuit (only 1 ATM)
 
Last edited by a moderator:
Are you doing an EICR or are you installing them.
 
You need to carry out a risk assessment as to whether the outlets are likely to be used for alternative purposes. If they are single phase I don't see an issue with just fitting rcbos.
 
You need to carry out a risk assessment as to whether the outlets are likely to be used for alternative purposes. If they are single phase I don't see an issue with just fitting rcbos.
It's highly unlikely these would be used for anything but due to location and use of warehouse,I know it's simple enough to change to rcbo but if it's not required there's no need.
 
It's highly unlikely these would be used for anything but due to location and use of warehouse,I know it's simple enough to change to rcbo but if it's not required there's no need.
You would need to carry out a risk assessment to quantify this and that is likely to be impossible as there are so many factors you cannot foresee. Alternatively get written acceptance from a responsible person or the person ordering the work outlying your reasons and their authorisation for omitting additional rcd protection. Easy route, fit rcbos.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
16amp 230 3pin sockets and rcd's
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
Dannyg8810,
Last reply from
westward10,
Replies
7
Views
1,690

Advert