Hi guys,


I have brain freeze and need some help!


I'm currently looking to run in a radial socket outlet circuit to a bedroom from a spare way in the consumer unit. The total circuit length will be approx 10 meters of 2.5 t&e. The supply is a TNC-S arrangement with a Ze of 0.13ohm (by direct measurement). The circuit protection is by way of a 20amp Type B BSEN60898 mini circuit breaker. NO RCD!!


Normally I would just follow the typical values in the OSG. This time though, I decided to just calculate it... Have to keep doing it once in a while or I'll forget!! :-/
The cable itself is fine (obviously) until I check the cpc size using the adiabatic equation. Can someone tell me if I've got this right? :-/


Ze = 0.13


R1+ R2 = 0.23 (adjusted for temperature @ 10 x 19.51 x 1.2)


Zs = Ze + R1 + R2
= 0.36


230/0.36
= 639A


K factor = 115
Assuming instantaneous time of 0.1sec


S = sroot(639*x0.1)/K
= 1.76??


Thanks in advance! :-)
 
i see where 639A has come from...

but you are looking for the fault current needed to acheave a .1 to 5 sec disconnection time...aren`t you...it aint 639A...is it
 
  • Like
Reactions: 2 people
looks like youre gonna need a cable with at least a 1.75mm cpc , which will be 6mm t&e ;-)


or maybe look at time current graphs for a 20a mcb ............


which will probably end up giving you a min cpc size of around half that.
 
  • Like
Reactions: 2 people
Don't forget the RCD.
 
Lets end this now, a 2.5mm2 cable to a socket as a single radial to a bedroom 10 mtrs away from the dist board?? yes okay get on with it, 16 amp mcb and you will be fine, fluck the calculations on this occassion.
 
Residual clot device
 

Attachments

  • RCD.jpg
    RCD.jpg
    8.4 KB · Views: 140
What about that RCD thingy though? Should I turn my fridge off before running this cable?! :-/ you're all confusing me now!! :-((
 
Gasp, you don't mean?? you do mean?? what with the 5wws, Glenn that is harsh LOL
i`m having a quiet, peaceful sunday....a gentle stroll through the forums....

i may feel different later on mind....
 
Hi Paul as your figure calculated using the adiabatic equation will not get a corresponding figure of t from the time / current graph you can obtain the I2t energy let through figure from your MCB manufacturer, you can then substitute it into the adiabatic equation.
The I2t figure for a crabtree starbreaker 20A type B 6K mcb is 22260 put that figure into the adiabatic .
Square root of 22260 / 115 will give minimum size cpc of 1.3mm.
 
  • Like
Reactions: 2 people
Hi Paul as your figure calculated using the adiabatic equation will not get a corresponding figure of t from the time / current graph you can obtain the I2t energy let through figure from your MCB manufacturer, you can then substitute it into the adiabatic equation.
The I2t figure for a crabtree starbreaker 20A type B 6K mcb is 22260 put that figure into the adiabatic .
Square root of 22260 / 115 will give minimum size cpc of 1.3mm.

Thanks for reminding me of this; they list I²t figures in the technical section at the end of their catalogue. As it happens, I generally use Crabtree Starbreaker, but does anyone know whether these figures are typical for other makes of BS 60898 circuit breakers?
 
  • Like
Reactions: 1 person
HandySparks

there is a reference table for minimum size cpc when using energy limiting class 3 mcb in onsite guide, table B7 page 120.
 
  • Like
Reactions: 2 people
I hate this forum!!


One of the reasons I never use it, is there's far too many egotistical smart arses on it who are only here to measure the length on their dicks with each other!


Thanks Silverfox1 for the feedback, it's much appreciated! At least there's someone willing to take the time to give a sensible answer!...........


Now to the admin,


Please delete my account, your forum is a disgrace, and seems only to serve very little purpose other than to serve up illiterate people trying their very best to sound clever!


Tedious and off putting!!
 
I hate this forum!!


One of the reasons I never use it, is there's far too many egotistical smart arses on it who are only here to measure the length on their dicks with each other!


Thanks Silverfox1 for the feedback, it's much appreciated! At least there's someone willing to take the time to give a sensible answer!...........


Now to the admin,


Please delete my account, your forum is a disgrace, and seems only to serve very little purpose other than to serve up illiterate people trying their very best to sound clever!


Tedious and off putting!!
come on Paul..
i gave you a reasonable answer...
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Adiabatic question
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
31

Advert

Thread statistics

Created
Paul_K,
Last reply from
Marvo,
Replies
31
Views
3,799

Advert