P
Paul_K
Hi guys,
I have brain freeze and need some help!
I'm currently looking to run in a radial socket outlet circuit to a bedroom from a spare way in the consumer unit. The total circuit length will be approx 10 meters of 2.5 t&e. The supply is a TNC-S arrangement with a Ze of 0.13ohm (by direct measurement). The circuit protection is by way of a 20amp Type B BSEN60898 mini circuit breaker. NO RCD!!
Normally I would just follow the typical values in the OSG. This time though, I decided to just calculate it... Have to keep doing it once in a while or I'll forget!! :-/
The cable itself is fine (obviously) until I check the cpc size using the adiabatic equation. Can someone tell me if I've got this right? :-/
Ze = 0.13
R1+ R2 = 0.23 (adjusted for temperature @ 10 x 19.51 x 1.2)
Zs = Ze + R1 + R2
= 0.36
230/0.36
= 639A
K factor = 115
Assuming instantaneous time of 0.1sec
S = sroot(639*x0.1)/K
= 1.76??
Thanks in advance! :-)
i see where 639A has come from...
but you are looking for the fault current needed to acheave a .1 to 5 sec disconnection time...aren`t you...it aint 639A...is it
Reactions: 2 people
looks like youre gonna need a cable with at least a 1.75mm cpc , which will be 6mm t&e ;-)
or maybe look at time current graphs for a 20a mcb ............
which will probably end up giving you a min cpc size of around half that.
Reactions: 2 people
Don't forget the RCD.
Lets end this now, a 2.5mm2 cable to a socket as a single radial to a bedroom 10 mtrs away from the dist board?? yes okay get on with it, 16 amp mcb and you will be fine, fluck the calculations on this occassion.
Residual clot device
What about that RCD thingy though? Should I turn my fridge off before running this cable?! :-/ you're all confusing me now!! :-((