400amp bs88 fuse blown 3 times in a year, building is a school and is feeding submain board, not an overload problem, any1 any thoughts for course of action?
 
If it isnt an overload fault, then it must either be a short circuit fault, or poor quality fuses.

You need to narrow the fault and the time it happens down a little, and make some deductions from that.
 
Nice thread succinct and to the point, maybe a short intro will get some more answers
 
  • Like
Reactions: 2 people
Get your tester out, if it is not overcurrent, then must be short circuit?.
 
i'd be looking very closely at the main switch's contacts , latching prongs , & fuse carriers.
 
I'm assuming it's 3 phase, is it the same phase that's going down each time? What is the loading/phase, what is it feeding etc, etc, etc, more info! We demand it! :)
 
Why do you consider it not an overload issue? - have you calculated the submains demand and confirms it is impossible to draw this amount of load?

What are your test results for the submains supply?
What is the fuse cascading down to? (discrimination)
What is the nature of submain 1ph 3ph?
If i have confused you here or even educated you to the basics you should already know and have done then go back to house bashing and give it to a competent Electrician with experience of larger installs.

Harsh i may be but with a short quick question like that and no info' it screams out that you are in too deep! otherwise you would have provided us with relevant info.

Ill happily be corrected if you will be so kind and forthcoming with the info i requested.

Edit - title Big Bang is this what happened did someone hear this - suggesting a short!
 
Last edited by a moderator:
What type of cable is the sub main and what is the run like to the sub board
 
Sounds like a job for Brendon Grace.
 
Could be single phasing as Biff is implying due to poor contact(s), if so replace all 3 fuses as the others could have been weakened and you'll just be chasing your tail. Above all you must get your test gear out and investigate!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
belfast

Thread Information

Title
big bang
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
meercat,
Last reply from
Deleted member 72666,
Replies
10
Views
1,331

Advert