I can't find cable Calcs for 16mm armoured cable reference method B. 2 cables.
Page 362 covers reference method C-E but where did A and B go?
 
not usual to install SWA method A or B.
 
SWA is not normally installed in method B and so no data is given in the regulations for that method. Which particular installation method within B are you planning to use?
 
I agree, that seems only option.
I was hoping if I could find method B it would top 100A, but to be on safe side I'll put 80A fuse in switchfuse.
 
I agree, that seems only option.
I was hoping if I could find method B it would top 100A, but to be on safe side I'll put 80A fuse in switchfuse.

That was not a serious suggestion! I thought the smiley at the end (and the obvious) gave it away

You appear to be doing your calculations incorrectly.
You need to calculate Ib then select In which you then apply de-rating factors to. Once you have the de-rated Value you then select a cable size which has a ccc greater than it. Then calculate the VD and predicted Zs to confirm compliance.
You do not start with the cable size and work backwards from there.
 
Last edited by a moderator:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent

Thread Information

Title
Cable Calcs
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
8

Thread Tags

Advert

Thread statistics

Created
Michaelwgroves,
Last reply from
davesparks,
Replies
8
Views
1,545

Advert