As above ,does any of the following work require a minor work cert,

changing MCB's, changing sockets, fitting CU blanks, filling CU holes with intumescent sealant (CU not to IP rating )

all noted during EICR's
some FI's which turn out to be loose wires in circuits

This is Scotland ,commercial premises, The Guidance from building control is vague to say the least
 

SparkyChick

Staff member
Mod
Esteemed
Supporter
Reaction score
7,996
I would issue a minor works for changing an MCB... assuming it's a rating change just to demonstrate the circuit complies with the maximum Zs requirements of the device. For the loose wires, you could issue a minor works just to record the test results to demonstrate you've fixed it.

The rest... no, because you're not changing a circuit, but you could write a report which explains what you've done to resolve the noted issues.

I don't know anything about the specifics in Scotland, but I would apply what I've said here in Wales or in England and would expect it to be sufficient to demonstrate that the works have been carried out.
 

timhoward

-
Esteemed
Arms
Reaction score
7,136
I agree.
A new MCB needs a MWC to record the fact that you've examined the circuit and are confirming that the conductor sizes are appropriate for the new device, the Zs is ok (as SparkyChick said) and the test results indicate you have reconnected something that is provably safe.
If the FI's for loose wires affected test results (which I presume they did to be detected in the first place) then I'd record those circuits too, so the next person has a set of readings for when you've finished (as opposed to when the EICR found the problems).
 

Petej999

Esteemed
Arms
Reaction score
328
As above ,does any of the following work require a minor work cert,

changing MCB's, changing sockets, fitting CU blanks, filling CU holes with intumescent sealant (CU not to IP rating )

all noted during EICR's
some FI's which turn out to be loose wires in circuits

This is Scotland ,commercial premises, The Guidance from building control is vague to say the least
Yes
 

Reply to does this need a minor works cert in the Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
I'm pulling my hair out trying to get a definitive answer for the following query. I'm trying to upgrade mcbs in a board and that we have been...
Replies
9
Views
1K
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
71K
A
Sample Questions C&G 2392-10 Certificate in Fundamental Inspection & Testing - paper 2 ( 1 ) The person who tests and signs the Electrical...
Replies
20
Views
25K
Deleted member 26818
D

New Posts (Please Reply)

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top