As above ,does any of the following work require a minor work cert,

changing MCB's, changing sockets, fitting CU blanks, filling CU holes with intumescent sealant (CU not to IP rating )

all noted during EICR's
some FI's which turn out to be loose wires in circuits

This is Scotland ,commercial premises, The Guidance from building control is vague to say the least
 
I would issue a minor works for changing an MCB... assuming it's a rating change just to demonstrate the circuit complies with the maximum Zs requirements of the device. For the loose wires, you could issue a minor works just to record the test results to demonstrate you've fixed it.

The rest... no, because you're not changing a circuit, but you could write a report which explains what you've done to resolve the noted issues.

I don't know anything about the specifics in Scotland, but I would apply what I've said here in Wales or in England and would expect it to be sufficient to demonstrate that the works have been carried out.
 
I agree.
A new MCB needs a MWC to record the fact that you've examined the circuit and are confirming that the conductor sizes are appropriate for the new device, the Zs is ok (as SparkyChick said) and the test results indicate you have reconnected something that is provably safe.
If the FI's for loose wires affected test results (which I presume they did to be detected in the first place) then I'd record those circuits too, so the next person has a set of readings for when you've finished (as opposed to when the EICR found the problems).
 
As above ,does any of the following work require a minor work cert,

changing MCB's, changing sockets, fitting CU blanks, filling CU holes with intumescent sealant (CU not to IP rating )

all noted during EICR's
some FI's which turn out to be loose wires in circuits

This is Scotland ,commercial premises, The Guidance from building control is vague to say the least
Yes
 

Reply to the thread, titled "does this need a minor works cert" which is posted in UK Electrical Forum on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
does this need a minor works cert
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5
Unsolved
--

Thread statistics

Created
neilyboy,
Last reply from
littlespark,
Replies
5
Views
1,499
Back
Top