What 'guarantee' do they give exactly?

They are shirking their responsibility by saying it was never TNS, although no one can prove it I bet it was. The mood and time of day they turn up has more effect on the out come than rules.
 
They are not shirking their responsibility if this is, as I suspect, a DIY job. Put it this way, if I install a circuit in your neck of the woods are you going to come out for free to repair it if something goes wrong?
 
hang on. just seen the pics. that BS951 may be a DIY jobby, but the corroded green clamp above it is a DNO fitted TN-S. so it's up to DNO to sort it FOC. end of.
 
  • Like
Reactions: 1 person
hang on. just seen the pics. that BS951 may be a DIY jobby, but the corroded green clamp above it is a DNO fitted TN-S. so it's up to DNO to sort it FOC. end of.


This?
photo.JPG
 
Yep that verdigris copper clamp was the original DNO clamp. Some clot has transferred the sheath earth to a BS 951 clamped to what looks like the the steel tape armouring!! Get the DNO back, all that needs to be done is that original copper clamp removed and replaced with either a Hepworth clamp or a constant force spring clamp, and the earthing cable reattached to the chosen sheath clamp
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earthing of TN-S: who should pay?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27

Advert

Thread statistics

Created
Etuj,
Last reply from
Engineer54,
Replies
27
Views
2,654

Advert