Brightspark2
Hi,
I conducted an EICR last week on a three bed property with a large extension.
- Broken earth on two lights downsatirs
- No ZS readings possible on the upstairs lighting circuit at any of the accessories. Switch drops wired in twin red no earth.
- Ring main no continuity >2000 ohms on all conductors
- Ring main 0.03 N-E 0.13 L-E 6.6 L-N IR readings
- 80 volts on switch wires of two seperate circuits
- 70 volts on ring earth
If you can't get a Zs at any accessories is there a CPC in this circuit?...all acc are plastic...
Ring main could actually be radials or 1 radial with a spur from the CU...
False reading??? Is there a load possibly still connected?...
Last 2 as mentioned could be induced voltage...