Hi.

Looked at a job this morning for remedial work on an EICR. The inspection has noted the plastic consumer unit within the hallway cupboard and given it a C2 rating citing regulation 422.2. The flat is on the second floor so the hallway would be the primary means of escape for the occupants.

Otherwise though it's in fine condition and sited behind a fire door in a cupboard.

What is the definition of an escape route? I can't believe that this small hallway meets the criteria as specified under reg 422.2

What do you think?

(update) I have since bothered to look further into this. Seems regulation 422.2 and the changes under amendment 2 are referring to 'protected escape routes' As the flat hallway isn't one of these then it wouldn't apply in this instance so is not a C2.

Thanks
 
Last edited:
The IET don't seem to want anyone to post a link, so I've had snip it as an image.

IET.PNG

Escape route.PNG
 
Last edited:
Hi.

Looked at a job this morning for remedial work on an EICR. The inspection has noted the plastic consumer unit within the hallway cupboard and given it a C2 rating citing regulation 422.2. The flat is on the second floor so the hallway would be the primary means of escape for the occupants.

Otherwise though it's in fine condition and sited behind a fire door in a cupboard.

What is the definition of an escape route? I can't believe that this small hallway meets the criteria as specified under reg 422.2

What do you think?

(update) I have since bothered to look further into this. Seems regulation 422.2 and the changes under amendment 2 are referring to 'protected escape routes' As the flat hallway isn't one of these then it wouldn't apply in this instance so is not a C2.

Thanks
Since when is a plastic consumer unit a potential danger when its electrically safe.
potential danger examples, over sized protective device, loss of continuity of cpc, high Zs readings etc
anything giving rise to electric shock in a fault condition. Or risk of fire!
Plastic consumer units with good electrical connections do not just combust!
 
Hi.

Looked at a job this morning for remedial work on an EICR. The inspection has noted the plastic consumer unit within the hallway cupboard and given it a C2 rating citing regulation 422.2. The flat is on the second floor so the hallway would be the primary means of escape for the occupants.

Otherwise though it's in fine condition and sited behind a fire door in a cupboard.

What is the definition of an escape route? I can't believe that this small hallway meets the criteria as specified under reg 422.2

What do you think?

(update) I have since bothered to look further into this. Seems regulation 422.2 and the changes under amendment 2 are referring to 'protected escape routes' As the flat hallway isn't one of these then it wouldn't apply in this instance so is not a C2.

Thanks
It would be a c3 and that's only if it's in escape route.
 

Reply to Escape routes definition in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted...
Replies
20
Views
2K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
Many will by now have heard of the new requirements for private landlords, enacted under Statutory Instrument 2020 No. 312, known as ‘The...
Replies
48
Views
13K
I'm a Facilities Manager and not an electrician though I do have some electrical qualifications of some years ago. I wonder if anyone would like...
Replies
4
Views
8K
So, I've been trawling through every bit of info available on AMD 3, specifically info regarding non-combustible DBs in domestic premises. Others...
Replies
57
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock