The RCBO is tripping on the heating system.
It is actually an S plan plus.
There is a neutral to earth fault of 0.02Mohms, this was tested at the FCU on the load side, with the load disconnected from the FCU.

The RCBO can be on and the boiler has all its displays working, but when you press the boost button on the programmer, it trips immediately.

I am new to fault finding on heating systems. My thinking is to just start breaking down the circuit as I usually would with a fault on a lighting or socket circuit?

With an S plan, its a bit of a spider, with all its legs coming out of the one large junction box housing the wiring centre. Is it just a case of disconnecting each leg, one by one and testing for the N-E fault?

I.e. I may choose to disconnect the hot water valve from the wiring centre and test that first, then move on to a different component (thermostat, cylinder valve, programmer etc)

Thanks :)
 
I would go straight to the motor wires of the HW valve judging by what you have described. They do go.
You can change just the head of the valve (hopefully),
 
Which boost button is being pressed, hot water or one of the heating circuits?
 
  • Like
Reactions: HappyHippyDad
Which boost button is being pressed, hot water or one of the heating circuits?
I'm not sure. I'll be back there in 30 mins, and that will be one of my to do jobs, as then i guess I can eliminate the other 2 zones.
 
Is it immediate after the button is pressed or after a short time?(A few seconds)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
~
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Fault finding a neutral to earth fault on S plan?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
HappyHippyDad,
Replies
5
Views
314

Advert