As regards OSG on electrical apparatus distance from gas pipes.
I am running a gas bond on an outside wall. I was just going to p clip it close to the gas pipe itself.
Or cable tie it to the pipe??
No rules on distance when its a bonding conductor?? Thanks.
 
cable tie to gas pipe would be neatest, IMO. or you could pvc tube it.
 
You can bond on entry into the building if its easier and complies with current regs before any branch pipework. wherepractcable connection within 600mm of the meter union or at the point of entry to the building if the meter is external. just a thought if it makes your job easier.
 
As regards OSG on electrical apparatus distance from gas pipes.
I am running a gas bond on an outside wall. I was just going to p clip it close to the gas pipe itself.
Or cable tie it to the pipe??
No rules on distance when its a bonding conductor?? Thanks.
BS 6891:2005 Installation of low pressure gas pipework in domestic premises, clause 8.16.2 states:
Gas installation pipes must be spaced: ... at least 25mm away from electricity cables where pipes are up to 35mm diameter and 50mm away from pipes greater than 35mm diameter. Except where the gas pipe is a PVC wrapped type or a partition of non-combustible insulating material is fixed between them.

Note:- BS 6891 uses the words electricity cables. It does not make a distinction between cables that are designed to carry current under load conditions and those that carry current under fault conditions. IMO this means all electrical cables irrespective of function must be separated from gas pipes.
 
Last edited by a moderator:
IMO a cable of any sort....(except trace heating)...should be independantly supported,using another service to strap it to is not good practice.
 
Note:- BS 6891 uses the words electricity cables. It does not make a distinction between cables that are designed to carry current under load conditions and those that carry current under fault conditions. IMO this means all electrical cables irrespective of function must be separated from gas pipes.


What about point of connection of the bonding conductor to the pipe? Makes that regulation seem a bit silly IMO.


Cables should though, be individually supported IMO.
 
Last edited by a moderator:
  • Like
Reactions: 3 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Gas bond outside
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
067256,
Last reply from
Guest123,
Replies
5
Views
2,422

Advert