Hi,
I'm looking for some advice.
We are a garden irrigation company and I have an electrical background (up to 16th edition).
We're carrying out an installation in a garden and have damaged 5 armoured cables (one a fibre optic) with our trenching machine.

The cables in question were for a new install to an outbuilding and were not live. They were buried under soil about 75mm with no mechanical protection or yellow warning tape.

The electrical contractor has told the client that he cannot do resin joints as they won't be able to sign off the installation.

Any professional opinions on these points in relation to current regulations would be greatly received as the cost of repair is going to be high
and they're trying to put all the liability on us.

Many Thanks
 
Hi,
I'm looking for some advice.
We are a garden irrigation company and I have an electrical background (up to 16th edition).
We're carrying out an installation in a garden and have damaged 5 armoured cables (one a fibre optic) with our trenching machine.

The cables in question were for a new install to an outbuilding and were not live. They were buried under soil about 75mm with no mechanical protection or yellow warning tape.

The electrical contractor has told the client that he cannot do resin joints as they won't be able to sign off the installation.

Any professional opinions on these points in relation to current regulations would be greatly received as the cost of repair is going to be high
and they're trying to put all the liability on us.

Many Thanks
I would let your insurance deal with it.
 
Thats really bad luck. Were you informed there were cables in the garden ? - Could it have been reasoned that cables could be there, e.g. direct connection between 2 buildings. A metal detector may have picked these up but its a guess. Direct burial to 75mm is high risk , there is no specific "law" it is based on risk, typically we tend to bury minimum of 500mm for cables carrying power, goes up to 1000mm on farm land.
Resin joints would be the standard repair but the fibre may have to be replaced. of course a duct would have helped here but it really depends what was specified by the client and the original risk assessment done to bury them at 75mm. If the client took that risk, then they reap the reward.........
 
If the cables were for a new install, then someone should have known they were there, and whoever put them in should have buried them at the appropriate depth, with warning tape.

A CAT wouldn’t have picked them up with no power connected, but I don’t see how anyone can point the finger at you.
 
I am no specialist in liability but if you look at this:

TLC Electrical Supplies - https://www.tlc-direct.co.uk/Book/7.13.3.htm

and see what ’good practice’ looks like and then add in the requirement to record such underground cable runs for future reference a case might be made that you are not wholly responsible and thence liable for the damage to the cables in question. The cable contractor has not done as much as reasonably practicable to safeguard the cables and addressed adequately the risk that they could be damaged during their life by digging or piling and the associated grave risk to humans doing such digging etcetera…..It is most fortunate they were not live because applying the electricity at work regulations and H &S laws would put the cable contractor under severe scrutiny.
 
Last edited:
The cables in question were for a new install to an outbuilding and were not live. They were buried under soil about 75mm with no mechanical protection or yellow warning tape.

The electrical contractor has told the client that he cannot do resin joints as they won't be able to sign off the installation.

Any professional opinions on these points in relation to current regulations would be greatly received as the cost of repair is going to be high
and they're trying to put all the liability on us.

Many Thanks

The point I wish to address is their statement about not being able to do resin joints... unless I'm much mistaken, there is absolutely nothing in the regulations that would prevent them from signing off a cable with a resin joint in it. If they are adamant this is the case, ask them which regulation this would contravene and how it would contravene it. If they cannot provide a valid regulation (we can check it) then they are quite frankly talking garbage.
 
Fibre repairs are possible but a very specialised job. If they were in duct then pulling a new one through would be the easiest/cheapest option I suspect (even if duct severed you can patch that). Otherwise if they were directly buried then I think there are companies who could do the equivalent of a resin joint repair for fibre, but cost trade off would need to be considered.

Without any warning given (but person who engaged you, or due care with tape and depth by installer) I would be arguing it is not my problem!
 
OP, can you keep us advised of developments, as most of us are of the impression that whoever buried the cables are the ones responsible.
Ie, not deep enough, not marked on drawings etc.
someone in planning this work must have known you would be digging holes where cables were recently buried.

Are you right in saying 75mm? That’s only 3 inches.
 
I may be transgressing a forum protocol so sorry and forgive me in advance - but I think freddo might have some useful advice.
 

Reply to Help with damaged underground cables in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’ve installed electric gates at a property. One of the issues I’ve had is I was unable to bury the cables at a sufficient depth as this would...
Replies
68
Views
8K
Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...
Replies
0
Views
1K
Hi I have been in the electrical contracting industry all my working life 40 years and became a member of the NICEIC in 2006. During this time I...
Replies
17
Views
2K
Partly cos I like to know everything... Partly because I'm a geek... And partly because we're going to have some electrical work done on the house...
Replies
16
Views
9K
Apologies for the complexity of this question, but there’s no easy way to explain it. This is a remote Norfolk house and workshops, developed...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock