If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Do you bond cable trays?
 
Not if they are in the bathroom (and its RCD protected)
 
  • Like
Reactions: Des 56
No,because I am not working with cable tray,but
My thoughts are,most situations probably not,but
If the specs asked for them to be bonded then bonded they will be,but
I would say that they also need bonding if they enter/exit a building
 
Wouldn't cable tray be an exposed conductive part, assuming you can touch it??

Exposed-Conductive-Part – Conductive part of equipment which can be touched and which is not normally live, but which may become live under fault conditions.

If there was an Insulation resistance fault with a cable on cable tray, there would be potential of it going live, so personally I would bond it, but it could be out of reach??? meaning it can't be touched and doesn't require bonding??

Either way, I would still bond it to be safe.
 
Wouldn't cable tray be an exposed conductive part, assuming you can touch it??

Exposed-Conductive-Part – Conductive part of equipment which can be touched and which is not normally live, but which may become live under fault conditions.

If there was an Insulation resistance fault with a cable on cable tray, there would be potential of it going live, so personally I would bond it, but it could be out of reach??? meaning it can't be touched and doesn't require bonding??

Either way, I would still bond it to be safe.
If it was deemed to be an exposed conductive part then you would earth it not bond it.
 
  • Like
Reactions: DPG and rolyberkin
Tray carrying insulated and sheathed cables would not be an exposed conductive part as the insulation and sheath are deemed to provide the same basic and fault protection as class II equipment 412.2.4.1
 
So SWA, Twin and Earth, MICC, SY, FP200 ext, Double insulated Flex, and Double insulated Meter tails would all be okay.

But if someone (Not me) was to run single cores or bare MICC, then it would need Earthing.
 
No,because I am not working with cable tray,but
My thoughts are,most situations probably not,but
If the specs asked for them to be bonded then bonded they will be,but
I would say that they also need bonding if they enter/exit a building
You think it is a good idea to bond a tray where it passes from a building, maybe into another.
 
Exactly what I have been reading haha. I didn't even know you can get bare MICC until I read that. Allways thought it was in an orange sheath.

Allways learning, that's what I signed up here for :)
 
Exactly what I have been reading haha. I didn't even know you can get bare MICC until I read that. Allways thought it was in an orange sheath.

Allways learning, that's what I signed up here for :)
I have installed bare, orange, red, black and white. Pay the manufacturer enough they will probably do you some pink.
 
Was there any particular reason for installing bare? or was it just down to cost / availability / Spec
 
Was there any particular reason for installing bare? or was it just down to cost / availability / Spec
Bare isn't common but you often see it in churches where the sheath tarnishes and becomes more aesthetically pleasing, in other words it blends to the surroundings.
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

westward10

Staff member
Admin
Esteemed
Supporter
~
Joined
Location
Northamptonshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
It's the weekend so....
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
westward10,
Last reply from
Barry White,
Replies
17
Views
2,000

Advert