AndyL
I understood from OP that there is FCU fitted, this give overload protection.True, if the 32A C/B can do the trick for 1.5mm cable?!?!. But the question was aimed that if the 32A C/B cant (and there isnt an FCU fitted for overload protection) how is fault protection now covered?
From reg 434.5.2 the 1.5mm cable will reach its limiting temp in about 1.6 seconds (assuming 160A fault current) As the CB will operate in about 0.1 seconds, at this current, fault protection is afforded