if i have got a 0.65Kw three phase motor does anybody know what i need to change thew settings to in the D.O.S starter??
 
Re: need help on what settings to put in a D.O.S starter for a 0.65Kw three phase mot

the overload on the started should have a dial on it that says Ir. It will have either a percentage of max current raing (so for exmaple 0.8 of In) or it will have exact current ratings. i would turn the starter to max, and then switch it on. measure the current and set the overload to 110% of that reading. Or another method is 110% of the FLA (which is written on the rating plate)
 
Last edited by a moderator:
Re: need help on what settings to put in a D.O.S starter for a 0.65Kw three phase mot

im sure on the dial it goes from .80 up to 1.2, i was told to add about 20% onto the 0.65Kw, so i set it to .80.
is that ok?
 
Re: need help on what settings to put in a D.O.S starter for a 0.65Kw three phase mot

i was taught to add 10% and i believe that when a similar thread arose on here, that was the general consensus.
 
Last edited by a moderator:
Re: need help on what settings to put in a D.O.S starter for a 0.65Kw three phase mot

Are you sure on the 0.65KW part...never seen one...0.55 and 0.75KW??

Scratch that just found an Exx proof one.......agree with the 110% FLC
 
Last edited by a moderator:
Re: need help on what settings to put in a D.O.S starter for a 0.65Kw three phase mot

yh im pretty sure its 0.65Kw, its in my AM2 test so they prob trying to mess me about :)
 
Re: need help on what settings to put in a D.O.S starter for a 0.65Kw three phase mot

Was the dial preset to the maximum just to make sure you did make adjustments??
 
Re: need help on what settings to put in a D.O.S starter for a 0.65Kw three phase mot

yea it was set to the maximum and the assessor said about adjusting it to suit the motor
 
Re: need help on what settings to put in a D.O.S starter for a 0.65Kw three phase mot

i haven't got one to hand but i would double check to make sure its not 0.65Kw/60Hz-0.55Kw/50Hz and i think you may have 2 different FLA specs, i may be wrong but i have definitely seen both on the same nameplate many times.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
need help on what settings to put in a D.O.S starter for a 0.65Kw three phase motor
Prefix
N/A
Forum
Electrical Tools and Products
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Aaron1988,
Last reply from
pmac10,
Replies
8
Views
2,839

Advert