Re: need help on what settings to put in a D.O.S starter for a 0.65Kw three phase mot
the overload on the started should have a dial on it that says Ir. It will have either a percentage of max current raing (so for exmaple 0.8 of In) or it will have exact current ratings. i would turn the starter to max, and then switch it on. measure the current and set the overload to 110% of that reading. Or another method is 110% of the FLA (which is written on the rating plate)
Re: need help on what settings to put in a D.O.S starter for a 0.65Kw three phase mot
i haven't got one to hand but i would double check to make sure its not 0.65Kw/60Hz-0.55Kw/50Hz and i think you may have 2 different FLA specs, i may be wrong but i have definitely seen both on the same nameplate many times.